OK…figured I will finish this off…
Basically I was trying to get people to think OUTSIDE the box when inspectors are looking at these things…yes, in the end it was to HELP the home inspector understand this better…not to have people give me freakin red boxes for trying to teach something ( tough crowd these days )
1.) The NEC is clear that the detached building needs a disconnection means, the 6 disconnect rule only applies IF the panel is " Suitable For Service Equipment " and will actually say so on the panels label.
2.) My example of a pool control system…which BTW is a “Sub-Panel” if it has OCPD located within it…would demand a " Disconnection Means " at the sub-panel for pools as well…unless of course it is " Suitable For Service Equipment "…panel and 6 breaker or less ( yeah fuses also )
3.) Just to keep you guys thinking…is their a exception to allow only (3) conductors to this panel…yep it is the same one as 250.32(B)(2) for detached garages…basically detached is…well…detached…but we will see that disappear down the road once your areas adopt the 2008 NEC.
4.) AS for 680.12…the breakers within the pool control system can serve as the disconnection means for the pool equipment…so thats all that is needed on that end as well…
Inspectors…if they RUN (4) conductors to the detached structure…then they have to use all (4) conductors…no if ands or butts…and trust me (4) conductors IS better…always is better in MY world of thinking.
Make sure they also have a GES for that detached structure…it will always need its own grounding electrode conductor and electrode…( of course we know of one exception for a single ciruit to a small shed so to speak…but we are talking BIGGER fish in the pond now arn’t we…yeah…sure we are.
so to round this topic out…the 6 disconnect rule does apply to both the service and subs…but read the SMALL little sections associated with it fully as that " Suitable For Service Equipment " just may change a few things…and just for educational purposes…do we know what makes it suitable for service equipment really…
Yep…the ability to bond the grounded bus to the enclosure and the grounding buss bar as you would in a normal service panel…chances are if it is a panel and has a bonding screw, strap or wire…it is " Suitable For Service Equipment".
Now…ENJOY life and stop giving me RED boxes on this thread for TRYING to help you people…GESSHHHH
PS. The image I posted shows a Disconnection Means to the right of the pool control panel…sorry as it is the best picture I could fine to show…also it was not finished yet I believe…see the 6 AWG for the ground rods hanging on the disconnect to the right.