I know this is wrong, just curious how everything still tested grounded?
The subpanel had a 3 wire feed, which typically means the neutrals and grounds are bonded. However, this one was setup like it did have a 4 wire feed, with the grounds separated and bonded to the panel, but there was no EGC connected to the bus. The conduit coming into the panel was also plastic…
So all the grounding conductors dead end at this panel, but everything still tested grounded…
What size is the OCP for this sub? What size are those feeders? Look about like #6 which is enough for 50 amps.
To me, that top ground looks like #10. There’s a chart for this but for a 50 amp breaker a #10 is sized appropriately. If it’s just #12 it is not.
So look at the upstream breaker. If it’s a 60amp breaker or larger, all the feeders appear to be small. Of course I’m not there, so they could be a size bigger than they look to me.
Couldnt tell… Too much going on. But this panel was fed by another subpanel right next to it. Service panel was just a disconnect at the exterior.
But its gotta be that larger 10 or 12 awg, as Dom pointed out, because there is one additional ground then there are circuits. And everything else in that panel is 14 awg
They are connected upstream, as is always the case. A common misconception among home inspectors is that the grounds and grounded conductors are isolated in sub-panels. They are not. The grounded conductor are all always solidly grounded. That’s why they are called grounded conductors. They are obviously tied together elsewhere in the system.