The home has 4 floors plus a basement. The panel is located in the basement and contains the GFCI breaker for the 6 receptacles pictured (+1 not in frame). These receptacles are located at the 4th floor rooftop terrace.
The NACHI Standard states:
“all ground-fault circuit interrupter receptacles and circuit breakers observed and deemed to be GFCIs using a GFCI tester, where possible”
What is your interpretation? Mash the button on your tester and run the stairs 7x to reset the breaker for each receptacle, test the breaker one time using the breaker test button, or do you have another option?
I am not sure, lol. This is new construction, and the other visible terraces didn’t offer much information. Outdoor entertainment systems? Outdoor kitchen/bar?
ndegaris
(Neil DeGaris, CMI® KY License # 102167)
9
Have your assistant check that all receptacles are powered on the 4th floor rooftop then call you in the basement and hit the test button on the breaker then have assistant re-check receptacles that power is in fact off… Easy Peezy!
I would verify they are all energized and properly wired, then trip and verify they are all de-energized, then go re-set the GFCI device and then verify they are all re-energized.
I checked each receptacle for power, then tripped one with my tester. Then, subsequently, I tested each one again and verified they had NO power.
Hobbled downstairs and reset the breaker. Manually test that breaker with the test button, and then leaped back up stairs and verified power had been restored to each receptacle.
Do you not carry multiple (backup) testers?
All told, I have prolly 6 total of various designs… (two are on my person, remainder in my Spare Tool bag).
Plug a Tester into ALL Outlets at once.
Confirm power ON at all outlets.
Hit Test button in Panel.
Confirm power OFF at all outlets.
Reset Breaker in Panel.
~Carry On~
How often do you replace your testers?
I replace at least two every year, which get rotated into the ‘back up plan’, and the two+ oldest/beat up get trashed! (Does not include damaged and Failing testers —> straight to the trash can)!
Like your Report Software and Digital File System… ALWAYS have a backup plan!!
I take it there were also GFCI outlets in the bathrooms and kitchen? Never seen that many exterior line source GFCI protected receptacles.
I have inspected various homes with GFCI outlets throughout the habitable spaces and outside the residence. (7) was the most.
I would test each GFCI independently.
GFCI Equipment Tripped breakers remained in the off position in the enclosure until I got to the last breaker. Once the last GFCI outlet was tested, I would go to the panel energise the breakers and test said GFCI outlets for current.
Other than that I tested GFCI outlets at the receptacle.
If I had a shadow he/she would do the footwork while we chatted on our mobile phones.