210.12 Arc-Fault Circuit-Interrupter Protection

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



icon_biggrin.gif


Present 2002 NEC Information:

210.12 Arc-Fault Circuit-Interrupter Protection.

(A) Definition. An arc-fault circuit interrupter is a device intended to provide protection from the effects of arc faults by recognizing characteristics unique to arcing and by functioning to de-energize the circuit when an arc fault is detected.

(B) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.

NECH: The definition of arc-fault circuit interrupter given in 210.12(A) explains its function.

The basic objective is to de-energize the branch circuit when an arc-fault is detected.

Arc-fault circuit interrupters are evaluated to UL 1699, Safety Standard for Arc-Fault Circuit Interrupter, using testing methods that create or simulate arcing conditions to determine the product's ability to detect and interrupt arcing faults.

These devices are also tested to verify that arc detection is not unduly inhibited by the presence of loads and circuit characteristics that may mask the hazardous arcing condition.

In addition, these devices are evaluated to determine resistance to unwanted tripping due to the presence of arcing that occurs in control and utilization equipment under normal operating conditions or to a loading condition that closely mimics an arcing fault, such as a solid-state electronic ballast or a dimmed load.

UL 1699 is the standard covering arc-fault devices that have a maximum rating of 20 amperes intended for use in 120-volt ac, 60 Hz circuits. These devices may also include the capability to perform other functions such as overcurrent protection, ground-fault circuit-interruption, and surge suppression. UL 1699 currently recognizes five types of arc-fault circuit interrupters: the branch/feeder AFCI, combination AFCI, cord AFCI, outlet AFCI, and portable AFCI.

Placement of the device in the circuit and a review of the UL guide information must be considered when complying with 210.12.

The NEC is clear that the objective is to provide protection of the entire branch circuit. (See Article 100 for the definition of branch circuit.) For instance, a cord AFCI could not be used to comply with the requirement of 210.12 to protect the entire branch circuit.

Section 210.12 requires that AFCI protection be provided on branch circuits that supply outlets (receptacle, lighting, etc.) in dwelling unit bedrooms. The requirement is limited to 15- and 20-ampere 125-volt circuits.

There is no prohibition against providing AFCI protection on other circuits or in locations other than bedrooms. Because circuits are often shared between a bedroom and other areas such as closets and hallways, providing AFCI protection on the complete circuit would comply with 210.12.

For your information only:



Quote:
This change requires all arc-fault circuit interrupters installed after January 1, 2008, to be of the combination type.

A combination type AFCI provides protection for both series and parallel arc faults.

A branch/feeder AFCI, referred to in the new wording in the second sentence of 210.12(B), is presently used to provide protection for the branch circuit.

It will continue to be recognized as meeting the requirements of 210.12 until January 1, 2008, at which time only combination type units must be used.

The technology needed to design and produce AFCIs that protect against both series arc faults and parallel arc faults is currently available but AFCIs commonly used to comply with 210.12 are not of the combination type.

The delayed effective date provides time for combination AFCIs to be designed, produced, and field tested, but also alerts the industry that it must address the issue within that time frame.

The exception was added to provide alternate means of accomplishing the desired protection. It is important to note that a metallic raceway or metallic-sheathed cable must be used and within 1.8 m (6 ft.) of the panelboard as part of this exception requirements.


Courtesy: www.iaei.org


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: bhendry
This post was automatically imported from our archived forum.



Hi Joe,


What are your thoughts on using one 15A AFCI breaker to supply/protect up to 3 separate bedrooms?

Regards,

Bill

![](upload://6W2YnX4wTESErcMziSzPMju9jcW.gif)


Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



bhendry wrote:
Hi Joe,

What are your thoughts on using one 15A AFCI breaker to supply/protect up to 3 separate bedrooms?

Regards,

Bill

![](upload://6W2YnX4wTESErcMziSzPMju9jcW.gif)


Hi Bill:

If the existing CB was replaced with the AFCI type that feeds the outlets you would have to settle for that.

But for a new wiring installation I would rather see at least two circuits for the 3 bedrooms. The instructions may have some restrictions?

Maybe there are limitations included by the manufacturer.


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Using the 3va per sq/ft 220 calc you could protect up to 600 sq/ft of “bedroom” with a single AFCI (assuming you were building to minimum code) but that is not a good design decision.


Originally Posted By: bhendry
This post was automatically imported from our archived forum.



Hi Joe,


Thanks. It just seems more elegant and simpler to have a separate circuit and AFCI for each bedroom. Also, turn one of the bedrooms into an office (lazer printers, etc) and another an exercise room (tread mill and what not) - common scenario I would think - and the one 15A branch gets loaded up pretty quick.

Regards,

Bill

![](upload://6W2YnX4wTESErcMziSzPMju9jcW.gif)


Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Greg Fretwell wrote:
Using the 3va per sq/ft 220 calc you could protect up to 600 sq/ft of "bedroom" with a single AFCI (assuming you were building to minimum code) but that is not a good design decision.


Unfortunately, that does not apply to dwelling units.

How many receptacles can you put on a single 15 amp AFCI? The real answer is "How many do you want?"

Can you put more 15 amp circuits on two 15 amp breakers than you can on one? No. You can put "as many as you want" on one, thus you cannot put more on two. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)

Typically, a good practice is to have no more than 13 points of take off available (13 single receptacle outlets, or 6 duplex receptacle outlets plus a single) on a 20 amp circuit. Using 180 va per outlet ( 180 va times 13 equals 2340 va divided by 120 volts equals 19.5 amps) for 13 outlets is within a 20 amp circuit. The 180 va also does not apply to dwelling units.

A 15 amp circuit would be 10 points of take off (5 duplex receptacle outlets). 180 va times 10 equals 1800 va divided by 120 volts equals 15 amps.

That is what we used to use down here, but that was done away with when we lost the South Florida amendments and fell back to the NEC when the Florida Building Code came into effect.

My preference would be to have one AFCI per bedroom, and that is simply because it makes it easier to isolate any given bedroom.

Another viewpoint is to have at least two circuits in each room, that way, if one goes out, there is still one on. the best way to do that is to put all the ceiling lights (and smoke detectors) of all the bedrooms on one circuit, then put the receptacles on another circuit, one circuit per bedroom.


--
Jerry Peck
South Florida

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Jerry you are ignoring the fact that you must provide 3va per square foot in article 220 for dwellings and these must be evenly distributed across the breakers. That is a defacto limit about how many square feet per breaker you have. You can put 1000 receptacles in that 600 square feet but you still have the 3va load minimum.


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Jerry unless it was different for FL it is 180 VA each single or for each multiple receptacle on one yoke.


But as you say that is not a dwelling unit issue anyway. ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Greg Fretwell wrote:
Jerry you are ignoring the fact that you must provide 3va per square foot in article 220 for dwellings and these must be evenly distributed across the breakers. That is a defacto limit about how many square feet per breaker you have. You can put 1000 receptacles in that 600 square feet but you still have the 3va load minimum.


I have never been convinced that we must provide 3va per square foot other than for the purposes of calculations.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



bbadger wrote:
Greg Fretwell wrote:
Jerry you are ignoring the fact that you must provide 3va per square foot in article 220 for dwellings and these must be evenly distributed across the breakers. That is a defacto limit about how many square feet per breaker you have. You can put 1000 receptacles in that 600 square feet but you still have the 3va load minimum.


I have never been convinced that we must provide 3va per square foot other than for the purposes of calculations.


Bob,

I think Greg missed the critical word in this.

220.30 Optional Calculation ? Dwelling Unit.


--
Jerry Peck
South Florida

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



I am just repeating what “AHJ” kind of guys said to me at the IAEI meeting when this came up. They said putting all the bedrooms on one AFCI would not get out of plan review and the article cited was “not evenly distributed across the General Lighting circuits”


General lighting load for a dwelling uses 220.3 (3va per sq/foot), no matter which computation method you use. ` Look at example D1(a)