mhix
(Matthew Hix, CMI MD -32331, VA - 3380000698)
1
Good afternoon all,
Just inspected a co-op unit with 3-phase power (10 awg, 4-wire).
The panel in the unit is a single phase panel rated for 100 amps (with 100 amp main breaker). Two of the service conductors are attached to the 2 main lugs, with the neutral on the neutral bar. The fourth wire is taped off, hanging in the panel.
The main disconnect is in the hallway, so the panel in the unit is a distribution panel. Hallway panel has three breakers, all in the on position, with no amperage rating on the breakers. Panel is sealed, so I can’t take off the dead front.
I don’t see many 3-phase panels, so it’s not my forte, but this all just seems wrong to me.
How should I describe the total amperage? Am I right to say the main breaker in the unit is over-fused?
I agree with Jim…something does not seem right here. First of all that panel looks to be MUCH newer than the hallway panel that is “supplying” it…Second, no way possible that 10 AWG is feeding an electric stove and dryer and other needs in that unit.
Just in terms of NEC minimums…it does not meet compliance with Section 225.39(D) at the least. So without going into too much detail I would indeed defer this one to be reviewed by a licensed electrical contractor…something smells with this one.
it just doesn’t fit…Add up if you will.
mhix
(Matthew Hix, CMI MD -32331, VA - 3380000698)
10
Thanks, all. I really appreciate your expertise and feedback.
The unit definitely doesn’t have enough power. The range is indeed on a 40 amp circuit.