AC differential temps
When I check for these temps I would hope that they are generally 17 18 degrees apart. I know that there are many things that our experts tell us that make all the difference when evaluating the AC differentials. Today’s inspection at the return air was 70 degrees and over the evaporative coil was 60 degree’s. I thought only 10 degrees…Todays outside temps was 89 degrees with 55% humidity, The t-stat was set on 68 and the t-stat temp said we were at 70 degees. The return line was beer can cold. I think that it is working great does anyone differ in their opinion?
Must we go through this all again?
Go back and read, then make your own decision based on your qualifications and assessment of the data you collected.
No one here can make an assessment for you from what you collected.
You can spend some money on an HVAC guy (I don’t recommend you telling someone else to spend the money on your uncertainty), or you can report that you turned it on at the thermostat and it blew air…
Gerald,
Did you actually check the temperature right at the coil?
Most inspectors check it at a supply register for many reasons, the main one being lack of desire to drill a hole or remove tape etc to access the coil area.
If you actually checked it at the coil I would say the system does need service. Even if you checked it at a supply register that is not cold enough air based on the other information you supplied.
When you feel of the suction line get into the habit of also feeling of the liquid/pressure line to make sure it is not real hot. Liquid line too hot almost always points to a dirty condensor coil or airflow issue in the absence of other symptoms.
What you detect at these lines and how you interpret it is based on lots of experience and conditions that day so you have to have lots of experience using the limited tools we, as inspectors, can use.
If you have a vacant house, real hot humid sunny day and the house is over 85 degrees inside, a 10 degree split seen at the registers may be all that it can do until the sun drops down later in the day.
Thanks for the input Bruce. The high pressure line was warm, not hot and The temp at the registers was virtually the same as at the coil and the RA. Unit was only 12 years old and obviously was cooling the house. I appreciate your help.
Oh and Dave thanks for…
First I would say we are checking whether it is functioning as designed. Does it cool or not. Yes there are variables which the experts get all up tight about but as a generalist it’s a simple question. When situations fall outside of a generalist scope we may call it out for further evaluation. But the plain and simple was even with a low temp differential it was obviously cooling well on that day. I don’t calibrate or do exhaustive testing on any other appliance…just report on what I see. I Don’t make more of it than what it is…
Gerald - Like David said …
What was the super-heat & sub-cooling? What SEER was the unit? After taking indoor drybulb, indoor wetbulb, did you plot this info to determine the RH% and expected TD (not measured but expected).
Then did you compare the SEER to the condensor TD to arrive at your desired SC?
Then did you take actual gauge pressures outside and convert them to saturation levels?
AND after taking the indoor dry bulb temperature and charting it compared to the outdoor temperature what was the SC.
Once he has that a home inspector is better equipped to talk reality’s.
I worked in the HVAC field and I only do temp drop test due to time constraints, I could spend an hour just on the air another hour on the furnace. If I get 15 - 20 degrees I am happy less or more I suggest having it serviced. I also give my clients a lesson about keeping the condenser level and clean to keep it the most efficient.
Furnace gets a exhaust gas test and the CO test of the supply air, this tells me a lot more than the type of flame it has. I can pretty quickly tell if there is good chance for a cracked heat exchanger and if the furnace is burning efficient.
I realize this is no what you meant, but if you want to save time why do you do a test that tells you nothing?
If you “worked” in HVAC, you are certified.
Why not just stick on a set of gages and actually get something that tells you what is going on instead of guessing?
Just asking…
I never check air temp as a stand alone test. There are too many things going on between the registers and the AHU. I can show you hundreds of thermal images as to why this testing is wrong, even if you did it right…
It’s a total wast of time, seeing you mentioned time.
It doesn’t take 2 hours to test an HVAC unit. If so, you need more practice.
As a Mechanical Contractor and Inspector, I say any one asking a Respectful Question deserves a Respectful Answer.
Just Saying…
Because we know it will piss you off!:twisted:
I see a lot of home inspectors say incorrect stuff about mold but I let it roll off. Calm down some, my friend.
Sorry, I don’t like to see wanna-be HAVC inspectors go off the deep end with their head stuck up their ***…
For one, it makes everyone in this industry look like an idiot.
Second, getting in trouble for following the blind and ignorant is not necessary to be part of the club.
As for respectful answers, they are posted in the archives for anyone that wishes to look it up instead of being a lazy *** and just ask the same nonsense over and over.
Seeing this is your #1 post and your a “mechanical contractor” jump right in there. No one is stopping your sweet answer.
You can start out telling me exactly the psychometric value of taking dry bulb temps to determine the working capacity of an HVAC unit. At what point I should call in another contractor to fix a definite issue with the equipment. I’m all for saving time in my inspections. I spent 9 hours on site at a home inspection today. I will likely spend 8 hrs writing the report tomorrow. If you can tell me how I can knock out 4 HVAC units by taking dry bulb temps, I’m all for it.
However, I must be able to tell my client that one unit has a low charge, one has a refrigerant leak at the reversing valve, one unit is leaking condensate all over the attic (and why), and the last unit has a detached return duct inside the wall…
I don’t want to hear nothing like "recommend further evaluation and repair of 4 HVAC units that appear not to be performing correctly as determined by taking dry bulb temperature measurements. My client didn’t pay me $1,300.00 for crap like that…
I do agree with David that dry bulb splits are not technically valid as a stand alone test or tool to gauge how well equipment is working, particularly with how most home inspectors get those readings.
However temperature splits can be a good indicator for an HI with some knowledge of how humidity and different types of equipment affects the readings and if the splits are taken correctly … in the ductwork airstream flow just before and just after the equipment … and if they do some other basic checks. Pretty much throw out the IR register readings, unless you are using that to supplement temperature measurements/splits at the equipment.
Getting splits is not the holy grail of cooling system inspections some may think it is, but I still think it provides useful information along with some other basic checks. Including checking: lineset temps (thats a big one, and you can just feel the lines); increase in condenser fan exhaust temp; condenser amp draw; lineset damage/kinks; ductwork leaks; ductwork insulation; adequately sized ducts (particularly the return); damaged/pinched ducts; clean filters, etc. All pretty simple and quick checks if you know what your doing.
With the family mechanical business we routinely do these basic checks (yes, including punching duct holes to get dry bulb TD readings with the fieldpiece) on an install or major repair. Granted we are also hooking up refrigerant gauges, checking for leaks with nitrogen, checking for contamination, checking superheat and/or subcooling, getting RH readings, etc. Buts those things are way beyond a basic home inspection.
JMO & 2-Nickels … :wink:
Temp splits: OK (I checked just for U-guys, from ir scans of the “leaking” supply and return registers").
Refrigerant pressures: OK
Suction Line superheat: OK
Think this new house will continue to cool for long?
May even get thorough the heating season, just wondering if this high heat bill is normal for a 7k sf house.
Next season the other three HVAC units may even mask the condition and they can run the thing into the ground with no referigerant…
It took me 3 passes by this unit before I “saw it”.
So even the best of testing may go unnoticed.
So why jack up your liability claiming your checking the HVAC (like I was being paid to do) when you don’t have to and really are not allowed to?
BTW: The suction line should be wet, but not with oil…
That looks like it would require “disassembly” to discover that referigerant oil leak. But I get your point, and it’s a good one. Everything can seem to be okay from some basic checks, but it doesn’t mean there isn’t a problem.
Home inspectors are not typically doing a technically exhaustive or invaisive inspection. However standards require an inspector to observe and report on the condition of a system. In order to do that effectively they should be doing some basic checks on the equipment, in order to help them make an assesment on the overall condition and operation of the system as a “generalist”.
In my book that includes getting splits at the equipment, with some knowledge of how ambient conditions and equipment types affect those readings … and if taken with a grain of salt. And if a home inspector doesn’t understand how humidity and types of equipment can effect the split readings, they shouldn’t take the readings and need some more training.
Shame on you Dave, setting a bad example. You should know better … :stuck_out_tongue: … If they are going to get splits (and you know they are) they should at least be doing them right … :wink:
I’m just trying to use relative temperatures so everyone else can compare with the wrong way of doing things! :slight_smile:
Disassembling: in many cases this refrigerant leak can be seen from the exterior by looking through the fan shroud.
In this particular case it took the removal of two screws.
Electrical components are also located under the same cover.
We take apart electric dead front covers to inspect, so I really don’t interpret this as a dismantling inspection.
Everyone seems to want to get into the HVAC inspection game. If they don’t want to take out two screws and “take a look” then they should just not do anything (they are not required to).
The same point I tried to make with taking temperature differentials. If you don’t want to go one step further and get it right, don’t do it at all.
To reiterate; in this example, as an expert I was unable to detect an equipment deficiency through temperature differentials. I located and identified a refrigerant leak without the use of any equipment, (even a flashlight). This means that “anyone can do it”. You simply need to know where to look, and what you are looking at. It is the same as taking temperatures and taking them from the proper location (which is your point).
It is just so tiring to listen to people try to justify a test procedure that is inaccurate, when they could do it right or not do it at all with very little effort.
[size=2]The most irritating part is the reason why they do this. They want to promote themselves as an overqualified home inspector but are unwilling to learn and do what is necessary and they harbor inaccurate information spewed out by unqualified home inspector trainers.
[/size]
If you are talking about taking out several screws on the condenser service access cover to gain access to that area I am all for it … similar to removing the access cover on a furnace or panel. You just have to make sure power is off before doing that, and don’t disturb anything inside.
That just looked like a view from removing more that a service access cover, which the typical home inspector really shouldn’t be doing in my opinion. My bad if that wasn’t the case … :wink:
And I wouldn’t expect that splits would have anything to do with the issue on that unit (unless it had been leaking for a while, and was low on refrigerant). I just happen to think that splits are useful for an HI doing basic checks of a cooling system, along with other basic checks that should be done as part of a typical home inspection, as long as the conditions that can affect the measurements are known and it’s taken with a grain of salt.
Hmmm. I wonder if Someone needs a Nap :cool:
He can be a little testy sometimes with a few of the posts that are made, where some people are way off. Thats just Dave.
How about your input and thoughts on the issues as a fellow mechanical contractor.
Yea, I need a nap from posting the same answer over and over generated by home inspector trainers that don’t know what they are teaching, and are teaching stuff that is outside the scope of the job to begin with.
Seeing your a fresh face, you are more than welcome to enlighten us on you perception of “reality” in the HVAC industry.
Robert uses splits in conjunction with other observations and measurements. There is nothing wrong with that. But when these guys call in an HVAC contractor because of a 10 degree split and can’t even provide information about if the sun is up…
…that’s another issue.
If you think I should coddle these guys after years of trying to explain the HVAC theory, don’t hold your breath. All the information is here for the search engine. There are links to my web site that goes through this stuff with a fine tooth comb.
Just Search Goggle: Should home inspectors inspect HVAC equipment?