This new section should ensure that grounded (neutral) conductors terminate within the panelboard to an individual terminal. This has been a UL requirement (UL Std. 67 – Panelboard Standard ) for some time, and the addition to the NEC is intended to bring this information to the installers. Technically, this is covered by 110.3(B), which requires all equipment to be installed in accordance with the manufacturer’s installation instructions and markings, but nobody knew it existed. UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment grounding conductors to terminate on a single terminal, if the terminal is marked for this purpose. Figure 408-3
The intent of this requirement is to ensure that the grounded (neutral) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in the destruction of electrical equipment and fires from overvoltage.
408.21 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Thanks to Mike Holt.
“If two grounded ( neutrals ) conductors are in the same terminal, and someone removes one of the neutrals, the other neutral may unintentionally be removed as well. If this happens on a multiwire circuit, it could result in excessive line-to-neutral voltage on one of the circuits…”
Thanks to Paul Abernathy
It never has been permitted technically by UL67 and under NEC 110.3(B).
It was clarified in NEC 408.21 In 2005, this reference was moved to 408.41
Even Mike Holt was confused by this issue.
Video link
Holt’s comment:
Switchboards and Panelboards
408.21 Grounded Conductor Terminations
Intent: This new section should ensure that grounded (neutral) conductors terminate within the panelboard to an individual terminal. This has been a UL requirement (UL Std. 67 – Panelboard Standard) for some time, and the addition to the NEC is intended to bring this information to the installers. Technically, this is covered by 110.3(B), which requires all equipment to be installed in accordance with the manufacturer’s installation instructions and markings, but nobody knew it existed. UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment grounding conductors to terminate on a single terminal, if the terminal is marked for this purpose. Figure 408-3
The intent of this requirement is to ensure that the grounded (neutral) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in the destruction of electrical equipment and fires from overvoltage.
The grounded conductor is a current carrying conductor. The grounded conductor is energized but has no potential (Voltage) between it and ground. If the connection is lost, there is a potential between the grounded conductor (which is no longer grounded) and ground. Anyone coming into contact with the white wire elsewhere in the house could be electrocuted.
The other major problem is that if the two grounded conductors are in contact with each other but have a loose connection to the bus bar, 240V could be impressed on 120V loads (if they are on opposite legs). That’s a common cause of electrical fires.