Hey Guys-
This is the first time I’ve seen the combo of aluminum and copper on the feeder. I wasn’t able to see a size label on the conductors. Any thoughts on whether or not those conductors are appropriate for 200 amps? Thanks.
Kenny
Hey Guys-
This is the first time I’ve seen the combo of aluminum and copper on the feeder. I wasn’t able to see a size label on the conductors. Any thoughts on whether or not those conductors are appropriate for 200 amps? Thanks.
Kenny
I have never seen that myself…Cool Picture…
Size looks fine for 200 Amps
AL would need to be 4/0 for 200 A service.
Copper would need to be 2/0.
Any thoughts on whether or not that’s a 4/0 AL conductor? Same for the SEC going to distribution panel???
Kenny
The Al and copper are fine as long as they’re properly sized as Micheal outlined. Hard to tell if those are #4/0 Al or not from the photo’s.