A nosing not less than 3/4" but not more than 1-1/4"shall be provided on stairways with solid risers.
A nosing is not required if the tread is 11" in depth.
Since the treads in the OP’s picture are carpeted, the riser height might exceed the maximum deviation of 3/8" and become a tripping hazard stepping on to the landing.
I’d be amazed if they caculated within 3/8" to get the correct riser height between carpeted tread and the wood finish floor on the landing. Of course when you step on that thick carpet, the effective riser height changes according to how much the carpet and pad compress, which varies according to how much you weigh and whether you’re wearing tennis shoes, high heels or swim fins, so there’s no good way to measure it.
It doesn’t seem like much, but I’d mention it as a possible trip hazard.
I had a seller tell they lost a sale because of that very reason, carpet to wood landing. The Inspector called it out :roll: it was just 3/8" off due to the carpet. The reason they walked was the contractors cost to fix. What a joke all around, people really need to communicate better as there was nothing wrong here except for the carpet not going up on the landing.
Riser differences can’t be more than 3/8-inch. Do you measure that with the carpet compressed, as if you were walking up or down the stairs, or non-compressed, as it is in the photo.