B-vent Roof clearance

Is this b vent from a gas furnace, supposed to terminate 2’ above anything within 10’?

It’s confusing, since it’s new construction and I see it done like this on most homes. 15874997405187918769892389455297|666x500

If that’s a 10/12 roof the IFGC says 2.5’ to 3.25’ height for cat 1 appliance. If you aren’t sure contact your local HVAC contractor.

No. A “B” vent is not a chimney.

IRC Section G2427.6.3 (503.6.4) Gas vent termination

Gas vents that are 12 inches (305 mm) or less in size and located not less than 8 feet (2438 mm) from a vertical wall or similar obstruction shall terminate above the roof in accordance with Figure G2427.6.3.

Contact a professional plumbing HVAC licensed contractor if this doesn’t help. Codes vary all over the country.

In a nutshell - it’s fine as-is.

I agree. (503.6.5) Gas Vent Terminations | UpCodes