bhartley
(Buck Hartley, CMI)
February 4, 2009, 12:21am
1
Would you recommend this flue be raised??
lkage
(Larry Kage, CMI)
February 4, 2009, 12:40am
2
Here’s a guide:
Table of Type B-Vent Rooftop Clearance Requirements
The 1992 Vent Sizing Tables require that all Type B gas vents terminate above the roof with a listed cap or listed roof assembly in accordance with the manufacturer’s instructions.
Vent caps 12" and smaller may terminate a distance above the roof if 8 feet or more away from a vertical surface as follows:
ROOF PITCH - rise/run in inchesMINIMUM HEIGHT*
Flat to 7/12 - 1.0 foot above the roof surface
7/12 to 8/12 - 1.5 feet above the roof surface
8/12 to 9/12 - 2.0 feet above the roof surface
9/12 to 10/12 - 2.5 feet above the roof surface
10/12 to 11/12 - 3.25 feet above the roof surface
11/12 to 12/12 - 4.0 feet above the roof surface
Continues to 21/12 pitch at 8.0 feet
Vent caps larger than 12" must be located at least 2 feet above the highest point and 2 feet higher than any portion of the building within a horizontal distance of 10 feet.
From: http://www.inspect-ny.com/chimneys/B-Vent_Chimneys.htm
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 1:26am
4
I am more concerned about the giant shadow of a robot I see in the picture,which is castings itself on to the roof image.
It appears to have a strange dome or bulb like contraption sticking from its head.
Almost pom pom like.
1 Like
bhartley
(Buck Hartley, CMI)
February 4, 2009, 3:26am
5
That is my stocking cap 25 degrees at 4 PM!!
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 3:29am
6
I know. hahahahaahaha
How far from the vents was the flue?
Looks ok.
We had this issue last month. (caused a debate)
bhartley
(Buck Hartley, CMI)
February 4, 2009, 3:42am
7
Thanks!! Approx. 12 inches.
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 4:02am
8
kshepard
(Kenton Shepard, CMI)
February 4, 2009, 4:07am
9
lkage:
Here’s a guide:
Table of Type B-Vent Rooftop Clearance Requirements
The 1992 Vent Sizing Tables require that all Type B gas vents terminate above the roof with a listed cap or listed roof assembly in accordance with the manufacturer’s instructions.
Vent caps 12" and smaller may terminate a distance above the roof if 8 feet or more away from a vertical surface as follows:
ROOF PITCH - rise/run in inchesMINIMUM HEIGHT*
Flat to 7/12 - 1.0 foot above the roof surface
7/12 to 8/12 - 1.5 feet above the roof surface
8/12 to 9/12 - 2.0 feet above the roof surface
9/12 to 10/12 - 2.5 feet above the roof surface
10/12 to 11/12 - 3.25 feet above the roof surface
11/12 to 12/12 - 4.0 feet above the roof surface
Continues to 21/12 pitch at 8.0 feet
Vent caps larger than 12" must be located at least 2 feet above the highest point and 2 feet higher than any portion of the building within a horizontal distance of 10 feet.
From: http://www.inspect-ny.com/chimneys/B-Vent_Chimneys.htm
Darn-o! I thought the 2/10 termination rule applied to all combustion vents for adequate draft reasons.
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 4:11am
10
Yeah, thats what I used to think.
I am still not 100 percent sure about if it should be 12 inch above that ridge in the picture.
Just looking at it makes you see down draft potential.
kshepard
(Kenton Shepard, CMI)
February 4, 2009, 4:14am
11
Are those tables in the current IRC?
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 4:18am
12
Good question.
I notice that you should check local codes and manufacturer guides.
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 4:23am
13
kshepard
(Kenton Shepard, CMI)
February 4, 2009, 4:28am
14
But if that’s Hart & Cooley’s guide, they’re just one manufacturer. Might their information not apply everywhere?
belliott
(Bob Elliott, 450.0002662)
February 4, 2009, 4:46am
15
Looks like a very good general information on B vents.
The diagram explains the general height rule very well.
sfetty
(Dave Fetty, CMI)
May 8, 2016, 5:10pm
16
lkage:
Here’s a guide:
Table of Type B-Vent Rooftop Clearance Requirements
The 1992 Vent Sizing Tables require that all Type B gas vents terminate above the roof with a listed cap or listed roof assembly in accordance with the manufacturer’s instructions.
Vent caps 12" and smaller may terminate a distance above the roof if 8 feet or more away from a vertical surface as follows:
ROOF PITCH - rise/run in inchesMINIMUM HEIGHT*
Flat to 7/12 - 1.0 foot above the roof surface
7/12 to 8/12 - 1.5 feet above the roof surface
8/12 to 9/12 - 2.0 feet above the roof surface
9/12 to 10/12 - 2.5 feet above the roof surface
10/12 to 11/12 - 3.25 feet above the roof surface
11/12 to 12/12 - 4.0 feet above the roof surface
Continues to 21/12 pitch at 8.0 feet
Vent caps larger than 12" must be located at least 2 feet above the highest point and 2 feet higher than any portion of the building within a horizontal distance of 10 feet.
From: http://www.inspect-ny.com/chimneys/B-Vent_Chimneys.htm
Thanks Larry! Bing found this useful thread.
jbernard
(John Bernard, TREC #9955)
December 27, 2016, 2:58pm
17
New construction. This stack appears to be too short, but I want to double check before getting into a discussion with the builder. Roof is 7/12 pitch. The stack is 22 inches tall and 21 inches from the roof and does not extend above the roof peak. Thoughts?
ccurrins
(Christopher Currins, CMI)
December 27, 2016, 7:13pm
18
Flat to 7/12 - 1.0 foot **above the roof surface. ** No problem.