I need a little education.


System grounding basicly protects the system from lightning and such, right? It directs the electricity towards the ground by a rod, copper pipe…, right?


Bonding does what? Connects components together? For what purpose, safety?

Lastly, subpanels should have floating neutrals, right? Why? What would happen if the neutral was tied to the ground?


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Grounding the neutral to earth helps protect against high voltages from lightning or utility high voltage faults imposed on the low voltage (240/120) on the customer side of the transformer.


This could be a 13,800 volt primary breaking and landing on the bare neutral of the overhead feed to a house.

Bonding the neutral to the panel and the rest of the metal objects likely to be energized provides a reliable fault current path back to the power source (the power company transformer) this is necessary to provide enough current to trip breakers quickly.

A sub panel that is has its neutral bonded to the grounding conductors will cause current that should be carried only on the neutral conductor to split and flow on both the grounding conductors and the neutral conductors.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: tlempe
This post was automatically imported from our archived forum.



Bob theres a great book that will answer all your questions its from Rex Cauldwell and its called wiring a house, it goes into detail on this subject


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



tlempe wrote:
Bob theres a great book that will answer all your questions its from Rex Cauldwell and its called wiring a house, it goes into detail on this subject


Gee I hope you meant Ed not Bob ![icon_eek.gif](upload://yuxgmvDDEGIQPAyP9sRnK0D0CCY.gif) as I have been wiring structures since I was 17 and I am 39 now.

I am pretty well versed on grounding and bonding, do you think I have made a misstatement?


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: roconnor
This post was automatically imported from our archived forum.



Bob … I am sure he meant to refer Ed to that book … icon_wink.gif


Ed ... I like how you separate out "grounding" and "bonding" in your mind. They are two completely different things. In fact, if you think of the green/bare wire of a circuit as a "bond wire" it might actually make more sense ...


--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee

I am absolutely amazed sometimes by how much thought goes into doing things wrong

Originally Posted By: tlempe
This post was automatically imported from our archived forum.



Sorry Bob, yes I meant Ed,I would never question anybodys experience anyway


Tim


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



I was just joking around anyway. icon_smile.gif


I got some PMs telling me I have to go to school.

If you are starting out in your knowledge of wiring methods that book is excellent advice.

If you would like to know more about grounding and bonding I would say get a "Soares Book on Grounding" I have heard a lot of good things about this book.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Geeez!!


Here are a few images from the Soares Book.
http://www.electricalmatters.com/gallery/Soares


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Joe, everyone you are taking things way to serious, I thought it was funny icon_lol.gif


Joe reverse the situation, you put up a post and someone suggests that you need to get a book on the code that would be funny.

Loosen up guys stop taking things so darn serious. ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

"The fool doth think he is wise, but the wise man knows himself to be a fool."


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Bob:


Here in the "Public" area, all and anything goes, and when I read your remarks above I too felt that your cage had been rattled.

Please consider what I have said here as an answer to your last message, and that now I understand your remarks.

Peace ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



I am sorry if I was not easily understood.


That said it has been my experience here at NACHI that there is a great deal of joking around and that makes it a fun place. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)


Peace. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)

Bob


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



I am attending an NEC Forum NFPA workshop on how to install AFCI’s. When I am able, I will make the information I received available.


Here is an image that will give us some idea of what some of the problems are, and although the industry has shown tests and videos and there are lots of Pros and Cons, many are going to support the use of this device:

This is a Technical Post:

![](upload://f8jcZMcCHEFJoc5BXuWmbj9ZQGA.jpeg)


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Bob


"I got some PMs telling me I have to go to school."

I will do it in 'public'-- you NEED to go to school. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)

Mike P.


Originally Posted By: tallen
This post was automatically imported from our archived forum.



I think you both need a time out. icon_razz.gif



I have put the past behind me,


where , however, it now sits, making rude remarks.


www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Ed


"Lastly, subpanels should have floating neutrals, right? Why? What would happen if the neutral was tied to the ground?"

Parallel conductors.

You would be allowing 'neutral' current to flow on the equipment grounding conductor.

This is why the water line connection (if it is an electrode) must be with in 5' of the entrance to the structure.

Mike P.


Originally Posted By: Ryan Jackson
This post was automatically imported from our archived forum.



Mike, didn’t Bob address that in his first post?



Ryan Jackson, Salt Lake City

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Ryan


Yes.

I just wanted to add the same problem occurs when the GEC is installed improperly.

Mike P.


Originally Posted By: roconnor
This post was automatically imported from our archived forum.



roconnor wrote:
Bob ... I am sure he meant to refer Ed to that book ... ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)

I meant that the book he referenced might be too "advanced" for ya (duck) ...


--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee

I am absolutely amazed sometimes by how much thought goes into doing things wrong

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



I can not say anything, Todd has not let me out of my “Time Out” icon_lol.gif


I think he forgot about me. ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

Bob


--