Bonding Screw in Subpanel

I’m not Robert but…

Not “grounded wires” moved. Grounded wires are neutral wires.

Equipment Grounding Conductors would need to be moved to a newly attached bus bar.

4 Likes

I was having a brain fart this morning. Thanks for slapping me.

1 Like

Hi everyone that has responded
Thanks for responding
I am still a little confused, the panel is a sub panel and should not be bonded, correct? The neutral wires are all on one bus bar, and same goes for ground wires. The grounding screw is not set into panel. Now the grounding conductor is not grounded to back of panel, which should be removed, a new bus bar installed and grounding conductor moved to new grounding bus bar, correct? Is that all correct?

Thanks
Todd

So if we start at the beginning since this is sub-panel it is supplied by a feeder. The feeder will be what’s commonly called a 4-wire feeder. That’s 2-ungrounded or hot conductors, 1-neutral conductor, and 1-EGC. Being that the neutral and EGC are separate conductors in the feeder they must terminate on separate buses. The neutral bus is isolated from the panel enclosure, the EGC bus is connected to the panel enclosure.

Since what’s shown in your photo is a PON panel (plug on neutral) the neutral bus must be connected on both sides of the panel to allow for the connection from a circuit breaker to the PON. So you would need to add a separate EGC bus bar connected directly to the panel enclosure, the feeder EGC would connect directly to that EGC bus. The feeder neutral would connect to the neutral bus. Only neutrals would connect to the neutral bus and only EGC’s would connect to the EGC bus.

3 Likes

Thanks Robert

I get all that but I don’t see the neutral line at all. There are two hot wires and the ground but not a neutral conductor in the sub panel shouldn’t there be one? At left side at the top of bus bar? I understand the rest now

Thanks so much
Hope I am not being a pain

Todd

I’m going to attempt to simplify @rmeier2 's response just a bit, to tailor it to you, as a newer home inspector.

  1. Since it is a sub-panel, it should have a 4-wire feed, two hots, one neutral, and one ground conductor.
  2. Neutrals and grounds should be separated in this panel, but in this particular panel, you can’t do it the way they did it. The busbar they used for the grounds can only be used for neutrals in this type of panel.
  3. A separate bus bar needs to be added for the grounds. This new bus bar will be attached directly to the panel enclosure and should only have the grounds connected to it.
  4. They didn’t turn in the green bonding screw, which is correct, but best practice is to remove it altogether, to avoid any confusion.

Hope that helps!

1 Like

Post of photo showing the entire interior of the panel.

2 Likes

A couple of other things that stand out, looks like one hot feeder might be Al, and one Cu? Assuming the Cu conductor is properly sized, the Al one might be undersized. Not sure if the top one just appears to Al though due to reflection. Also, looks like a ground was landed on the left bus, that should get moved to the new bus bar along with the other grounds. If it is not a ground, it is improperly colored.

1 Like

Hi All

Thanks again for all your help.

Have a wonderful evening
Todd

2 Likes