The bonding screw appears to be loose and not making contact with the panel. Would there be a reason to leave the screw loose in this service panel. What I see is the neutrals bonded to together with a jumper or strap and the equipment grounds together on the side bus. See pictures (And yes my standards require me to open the electrical panel when safe to do so)
Neutral not label with white tapeYeah there’s a reason, they forgot to tighten it.
No reason. Write it up! If there is no bus bar attached to the panel the only thing happening here is the panel case is not grounded, as it should be.
A wiggy would allow you to verify the absence of panel enclosure ground. One lead to hot other to panel enclosure.
I agree that it should be tightened if it is not a sub-panel. However, it is interesting they separated the grounds and neutrals onto separate busses (at least it looks like it, but hard to tell with the picture quality). Might just be the way they do things, but also could be they forgot to remove the crossover bar. Was there an exterior disconnect?
this service panel.
I’ll take that to mean there was no other disconnect upstream, in which case, you are on the right track. It is still interesting to me that they separated the grounds and neutrals onto separate busses. Not something that is done in my area unless it is a sub. But, nothing wrong with doing it that way.
Then the main bonding jumper (MBJ) which is the green screw must be fully tightened. Your second and third photos were too blurry to enlarge for a closer look.
Yes, i know I’m confused why this is starting to happen in my area more
Maybe prepping for potential future conversion to a sub? Or, maybe the electrician didn’t know at the time if it was going to end up being a sub.
If this were inspected the EI should have caught it.