I saw this service panel today and I cannot see that the neutral and the ground are bonded. it looks to me like it does not have a bounded neutral. Would you agree?
Thanks!
Until you get a photo posted… NO, it is not! (Better safe than sorry).
This is what I see…
If my head wasn’t screwed on, etc…
Picture now attached
1 Like
Typically a green screw will indicate the bond point, if I am understanding your question correctly.
3 Likes
I agree with Ryan.
From here it appears that the neutral bus is bonded to the panel via the green screw.
3 Likes
It looks correct from here, if that’s the main panel. Ryan pointed you in the right direction
2 Likes
I agree with Ryan, Kevin, and Christopher!
1 Like
Thank you all very much for your help!
1 Like
is this the service panel? Or a sub panel? It is only 100 amp, and if it is a subpanel, its wrong.
OP says…
1 Like