Is this panel correctly bonded?

First post on this forum.
I saw this service panel today and I cannot see that the neutral and the ground are bonded. it looks to me like it does not have a bounded neutral. Would you agree?
Thanks!

Until you get a photo posted… NO, it is not! (Better safe than sorry).

This is what I see…

If my head wasn’t screwed on, etc…
Picture now attached

1 Like

Typically a green screw will indicate the bond point, if I am understanding your question correctly.

3 Likes

I agree with Ryan.

From here it appears that the neutral bus is bonded to the panel via the green screw.

3 Likes

It looks correct from here, if that’s the main panel. Ryan pointed you in the right direction

2 Likes

I agree with Ryan, Kevin, and Christopher!

1 Like

Thank you all very much for your help!

1 Like

is this the service panel? Or a sub panel? It is only 100 amp, and if it is a subpanel, its wrong.

OP says…

1 Like