the course say it has to be 3 feet clear in the front and the sides but doesnt say that it has to be three feet above the window as well, i might be being overly specific but is that true?? like for example my arm is probably three feet long so according to those standards i could technically reach out and touch the power line if i wanted to
This old post might explain it clearly for you.
https://forum.nachi.org/t/service-entrance-clearance/59265
(A) Clearances
Service conductors installed as open conductors or multi-conductor without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.
Exception: Conductors run above the top level of a window shall be permitted to be less than the 900 mm (3 ft) requirement.
UpCodes
(A) Clearances
Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.
Exception: Conductors run above the top level of a window shall be permitted to be less than the 900 mm (3 ft) requirement.
(B) Vertical Clearance
The vertical clearance of final spans above, or within 900 mm (3 ft) measured horizontally of platforms, projections, or surfaces that will permit personal contact shall be maintained in accordance with 230.24(B).
(C) Building Openings
Overhead service conductors shall not be installed beneath openings through which materials may be moved, such as openings in farm and commercial buildings, and shall not be installed where they obstruct entrance to these building openings.
Bill & Robert have it… …
The first step to EVERYTHING is to fully understand the WHY something is required!
Not understanding is akin to grabbing that power line!
what counts as “an overall jacket”? like a metal conduit or something?
what counts as “an overall jacket”? like a metal conduit or something?
That is correct.
Not a conduit a cable. SE cable would be an example of a cable with an outer jacket. The multiconductor cable without a jacket would be something like triplex drop cable that the utility uses from the pole.
Thanks for all of the info! Always good info here.