Combined Flue
Is it OK for a LPG furnace to vent into a wood furnace’s flue?
No. …
Gas and wood venting requirements are not compatible at all.
Jeff,
No, No, No…
You must be playing “devils-advocate”.
In our part of the world, you never mix flue venting from the various fuels (ie:NG, LPG, Wood, OIL, etc.).
Well lets take a look and see what the code says:
International Fuel Gas Code 501.7.2 Connection to factory-built fireplace flue. An appliance shall not be connected to a flue serving a factory-built fireplace unless the appliance is specifically listed for such installation. The connection shall be made in accordance with the appliance manufacturer’s installation instructions.
**International Mechanical Code 801.10.2 Connection to factory-built fireplace flue. **An appliance shall not be connected to a flue serving a factory-built fireplace unless the appliance is specifically listed for such installation. The connection shall be made in accorance with the appliance manufacturer’s installation instructions.
Yes, if the furnace is designed for that type of installation and if it is in accordance to your county and state building codes.
Ummm…
I’ll go with the IRC on this one:
No solid fuel and gas in same vent . . . . . . . . . .2426.5.6.1
Jason,what counts the most in that particular situation is what Bruce stated in his last paragraph of his post.Always check the local codes being used if you are going to state code. Matt
Agreed, but most are based on the IRC are they not?