Didn’t mean to get you shook up, Tony, but it does change a few things.
First, in response to your concern with clay being suspect here; if this was caused by clay movement, there will definitely be at least one companion crack. Being in the middle of a long wall, you'd first normally be looking for two more cracks; one toward each end of that same wall. But, if this were from clay pressing on the wall, the center crack would be wide inside & tight on the exterior; from the photos yours looks to be the opposite of that. (crack looks tighter on the inside)
The other clay-caused scenario would be that part of the footing has settled, allowing part of the wall to tilt/drop. This action would be more in keeping with the V-shaped crack you have, but can only occur with at least one additional crack point.
Curing shrinkage cracks would likely be prevalent in pours done during cold weather, as many builders pour their mix far too wet and in cold weather often add hot water or calcium chloride to speed curing, however they really only accelerate the initial set, while full curing may take 30-60 days. Shrinkage cracks also do tend to appear near points where the is an expanded volume of concrete, such as this beam support column.
As to the extended measures in backing up this crack since it's on a full-depth wall, this includes the epoxy injection as mentioned before, but should be additionally reinforced with 1 to 3 vertical 4X4 I-beam columns. One column should be placed as directly over the crack as possible, preferably with an additional column no more than 5 feet to each side.
The columns have welded floor shoes with 2 holes in them; the floor is drilled at each hole and minimum ?" X 3" high-strength shoulder bolts are installed with anchoring cement or epoxy. The top of each beam is anchored into the floor framing with angle iron, blocking and/or sistered joists spanning inwards at least 6', widening the blocking in a "V" as it moves inward. (In other words you have blocking in 1 joist space at the beam, 2 joist spaces 16 to 24" away, 3 joist spaces 32 to 48" away, etc.) Angle iron is lagged, all blocking is glued and nailed. Beam height is determined by the maximum height available. (Depending on joist direction and clearance, beams may have to be cut to bottom of floor joists and anchored initially against angle iron.) The I-beam is placed as tight to the wall as possible, but walls are never totally flat and you want absolutely no voids behind the beam, so when the beam is placed it's first "buttered" with a product like full-flex mortar, then pressed to the wall and anchored.
Similar in many ways to other's methods, this is a total process developed by my Father & I which has proven 100% effective for over 20 years now.
I hope I've detailed the method in a way it's understood; let me know if I can clear any questions up. (Mark A., I've just passed along what amounts to a "trade secret" here....I hope you don't pass it on to Hague or whatever his name is, LOL)
P.S. Tony, are there any cracks appearing in the basement floor slab? If so, do any start/end near the same area of this wall fracture?
--
Do it right; Do it once