Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Gerry


This is a bad question. Sorry. And it will confuse more than it will help.

Mike P.


Originally Posted By: gbeaumont
This post was automatically imported from our archived forum.



Hi Mike,


You know, before I set this question I ran it past 2 very experienced inspectors in this field, who had no issues with it other than the "inspector speak terminology".

and also personaly I am very happy that 70 odd % of our respondents are getting it right. ![icon_exclaim.gif](upload://kW92MliyHA8ygoXI0UsgtBSn4ZO.gif) ![icon_exclaim.gif](upload://kW92MliyHA8ygoXI0UsgtBSn4ZO.gif) ![icon_exclaim.gif](upload://kW92MliyHA8ygoXI0UsgtBSn4ZO.gif) ![icon_exclaim.gif](upload://kW92MliyHA8ygoXI0UsgtBSn4ZO.gif)

Feel free to explain tomorrow why this is a "bad" question

Regards

Gerry


--
Gerry Beaumont
NACHI Education Committee
e-mail : education@nachi.org
NACHI phone 484-429-5466

Inspection Depot Education
gbeaumont@inspectiondepot.com

"Education is a journey, not a destination"

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Gerry


In your example I may 'bond' at the second building.

Mike P.


Originally Posted By: roconnor
This post was automatically imported from our archived forum.



Mike … That is not a separately derived system, even though the pic shows separate buildings. There is also a bond wire (EGC) shown as running with the feeder, so a N-G bond under 2002 NEC 250.32 would not be allowed.



Robert O’Connor, PE


Eagle Engineering ?


Eagle Eye Inspections ?


NACHI Education Committee


I am absolutely amazed sometimes by how much thought goes into doing things wrong

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Mike is correct we can bond at the second building in this example.


Most times I would choose not to, other times it is a better way to go.

The reasons are complicated and will only confuse the main point here. ![icon_confused.gif](upload://qv5zppiN69qCk2Y6JzaFYhrff8S.gif)

In dwelling units any panel that does not have the service disconnect should be isolated neutral.

However run a feeder from that dwelling unit to a separate barn, shed or garage and it is the installers choice if they bond or not.

250.32(B)(1) and 250.32(B)(2) are the relevant code sections.

I am sorry Jerry but I think it would be better if the graphic showed the two panels in / on the same structure / building.

If the graphic had the two panels in one structure the answer would be clear as shown they are two correct answers and neither one is necessarily better then the other.

Each method has good and bad points.

The correct answer to the grapic is not in the list of answers as the correct answer is either bond or don't bond.

Bob


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: roconnor
This post was automatically imported from our archived forum.



Bob … HI’s do run across sub-panels in out buildings and garages, so I thinks it’s something worth while discussing.


The pic shows the sub-panel in the separate building fed from a breaker in the service panel with a ground/bond wire (EGC) run with the feeders. So there should not be a N-G bond at the sub-panel. That would permit parallel neutral paths ... not good.

NEC 250.32(B)(2) allowing a N-G bond at a separate building would only apply if the was no ground/bond wire run with the feeder.


--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee

I am absolutely amazed sometimes by how much thought goes into doing things wrong

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



roconnor wrote:

NEC 250.32(B)(2) allowing a N-G bond at a separate building would only apply if the was no ground/bond wire run with the feeder.


Correct and as the installer I can choose not to run a grounding conductor, I can use the grounded conductor as the grounding conductor.

When the run is short running a separate grounding conductor is a great way to go.

If it is a long run it is more cost efficient and electrically more efficient to use the grounded conductor as the grounding conductor.

When a ground fault happens which is better electrically for a 100 amp panel. The code minimum 8 AWG grounding conductor or a 3 AWG grounded conductor for the fault current path?

I am more than happy to get in to this, but I have been trying to keep my answers shorter, less technical and with fewer code references. ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)

Bob ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



For what it is worth this subject grounding / bonding is very tough for electricians too.



Bob (AKA iwire)


ECN Discussion Forums


Mike Holt Code Forum

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



OK I retract what I said, once I look closely enough at that graphic it shows both a neutral and a ground between the panels in that case the neutral must be isolated.


If there was no EGC run with the feeder the neutral would have to be bonded.

I had just looked at the single line between the panels.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: roconnor
This post was automatically imported from our archived forum.



To find the bond/ground wire … look at the green wire on the right side of the service panel, which continues to the right side of the sub-panel. With this wire the sub-panel shown can NOT have a neutral-ground bond … the neutral MUST be isolated.


Without the pic I agree the question would be vague since it doesn't state the sub-panel is in the house and it is not known if that sub-panel is in a separate building where maybe a bond/ground wire was not run with the feeders.

As Bob pointed out it is okay to run a feeder to a separate building without the bond/ground wire and then have a N-G bond in the sub-panel. But ONLY if it's a separate building without a bond/ground wire run with the feeder.


--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee

I am absolutely amazed sometimes by how much thought goes into doing things wrong

Originally Posted By: Vince Santos
This post was automatically imported from our archived forum.



Ahhh…


I go the question right however...

I have learned something today. You guys are great! ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Desire is half of life, indifference is half of death.
--Kahlil Gibran

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Bob


You give up too easily. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)

There are two ungrounded conductors, a grounded conductor and an equipment grounding conductor ALL connected.

Mike P.


Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



1st one I got wrong in quite awhile…I never knew you had to isolate the neutral/ground in a subpanel if the feeders contain both neutral and ground.! icon_idea.gif



Wisconsin Home Inspection, ABC Home Inspection LLC


Search the directory for a Wisconsin Home Inspector

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Kevin


Good for you to be honest.

In your area grounding/bonding is very important.

In rural areas this can be very important to farmers.

Learn all that you can.

PS You do not have to be licensed to do EMF Consulting.

No I will not tell you what it is. Research it.

Mike P.


Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Deleted



Joe Tedesco, NEC Consultant


www.nachi.org/tedescobook.htm

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Gone icon_wink.gif



Bob (AKA iwire)


ECN Discussion Forums


Mike Holt Code Forum

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



This statement in a previous post of mine is erroneous. Please disregard it.


"There are two ungrounded conductors, a grounded conductor and an equipment grounding conductor ALL connected".

Mike P.


Originally Posted By: dfrend
This post was automatically imported from our archived forum.



Joe, Personally, I like seeing the different perspectives. Debate is a healthy way to learn. Sometimes, opinions have to made, and through the debate we can sometimes realize our opinions were misguided.


As for the diagram, doesn't matter as to copyright as long as Gerry did not plan way ahead of time to use it and it is for educational use. It is called "fair Use under the copyright laws.

From US Code title 17 chapter 1:
(I knew all that instructor training would come in handy ![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif) )

Quote:

Sec. 107. - Limitations on exclusive rights: Fair use



Notwithstanding the provisions of sections 106 and 106A, the fair use of a copyrighted work, including such use by reproduction in copies or phonorecords or by any other means specified by that section, for purposes such as criticism, comment, news reporting, teaching (including multiple copies for classroom use), scholarship, or research, is not an infringement of copyright.



--
Daniel R Frend
www.nachifoundation.org
The Home Inspector Store
www.homeinspectorstore.com

Originally Posted By: gbeaumont
This post was automatically imported from our archived forum.



Hi to all,


Sorry that I decided to pull this question but after realizing that I had used someone elses copywrited materials without authorization I felt it was only fair to undo the damage, besides it was taking me more time than enough to debate the ins and outs of copywrite law, than the issue was worth.

regards

Gerry


--