Hello everyone, Jacob, ME., here.
I also am new and working through the courses at InterNACHI.
I have some background experience working in construction
in various areas, but electrical is a weak spot for me, too.
I was looking at OP’s picture and I had two observations, as
I recently completed the Electrical Course.
I see several neutrals in one connection, and I’m wondering
if that is providing a solid connection to all those wires. I
recall a part of the Electrical Course saying something about
how the set screw wouldn’t be able to make a very good
connection when there is more than one wire inserted.
I circled the area where one neutral appears to be damaged.
That also causes me to question the ability of this component to
function correctly.
Please, anyone, feel free to correct me if I am mistaken. Also,
any advice or input is welcome.
Your eyes are better than mine.
I’ve never seen an EGC bus that was listed for that many conductors in a single hole. Generally it’s two or three with the number and sizes listed on the label in the panel.
I have an idea why that may matter. A single multiple strand cable is wound together a million times. Which in my opinion would certainly guarantee connectivity. Similar to a “pig tail” or “rat tail”. But, I need to disqualify myself, I am NO electrician.
Jeffrey, There are standard specifications for the manufacture of all wires, cables, and terminals. They take into account such things the ratio of cross-sectional area of the conductors, the cross-sectional area of the terminals, the ratio of the cross-sectional areas, heat dissipation properties, and so on. The size of the individual strands in a multi-strand conductor are also all the same size and metallurgy.
Components are tested for specific installation configurations. It isn’t possible to cover every conceivable arrangement. There are potential problems when there are different sizes and different metallurgy. To keep things simple, everything is rated for use in the way that it was tested and listed. As a practical matter, you could put multiple stranded conductors and probably not have a problem because there is a large margin for error with electrical equipment in general. But that’s another discussion.