GFCI's in the Kitchen

No it would not!
Read this thread…

“All commercial buildings/kitchens are required to have GFCI for refrigerators. See NEC 210.8(B)(2).
In a Dwelling Unit (house or apartment) refrigerators located inside the kitchen do NOT have to have a GFCI. See 210.8(A)(6), Exhibit 210.13, 210.52(B)(1), 210.52(B)(2), 210.52(B)(3), and Exhibit 210.28. If the circuit feeding the refrigerator outlet is branched to any other outlet, it must be a 20-A circuit. If the circuit feeding the refrigerator outlet is a dedicated individual circuit, than it can be either 15-A or 20-A.
In a garage or an unfinished basement of a Dwelling unit, the refrigerator must have a GFCI circuit. In fact ALL outlets must be GFCI in garages and unfinished basements. See 210.8(A)(2) and Exhibit 210.10.”