R2, What do you use there for a refrigerant?
Good morning guys!
It’s early and I was up late and I’m working on my first cup of coffee. I’m not getting the questions/issue for some reason (my voice recognition software won’t recognize my voice either, so aliens probably abducted me during the night!).
These are the questions I see here:
A heat pump is not efficient. My question to answer is why.
You are all adding good pieces of information , but let me put it all together.
A heat pump absorbs heat from one location and displaces it elsewhere. In order for the equipment to absorb this heat there must be a temperature differential. We look for a 30° temperature differential between the refrigerated coil (which is the outdoor coil in the wintertime) and the outdoor air. As the outdoor air goes down, so will the refrigerant pressure and temperature. This 30° split generally remains intact.
The problem with efficiency arises when btu’s are less in the outdoor air. If you think of heat as a substance to be absorbed or collected, this may make more sense. If there is less BTU in the outdoor air, there is less to be moved to the indoors.
The second part of this is that the temperature difference between inside the house and outside the house becomes greater as the outside temperature falls. The heat transfer rate is Q=UADelta T. As the temperature difference between indoors and outside increases, heat/BTU passes through the house wall/roof at a greater rate(one multiplier per degree Fahrenheit). To maintain a constant indoor temperature, this amount of loss must be made up by the HVAC equipment. As there is less available BTU in the outdoor air, its not possible to absorb a sufficient amount to maintain the indoor air temperature. Thus, auxiliary heat is installed.
Another efficiency issue which may not be realized is that the power consumption used to run the equipment in the wintertime is dramatically reduced as the BTU availability in the outside air falls. Also, All electrical power utilized to run the compressor is change from electrical to mechanical energy thus producing heat which is absorbed by the refrigerant and sent back into the house. So, actually the system is quite efficient in using electrical power (it’s just not sufficient to keep you “comfortable”). In the summer, the unit may draw 45 amps. In the winter it may draw 6 amps. So, even though it runs continuously, it takes less to operate.
Heat pumps are very efficient when operating in temperate temperatures, such as the spring and fall where there is sufficient heat in the outdoor air and conditioning of the indoor air is required for comfort. This is where you save money. These savings must be averaged and is absorbed by the entire heating season’s use, and depending on where you live may become drastically reduced. In essence, you are operating a straight electric furnace in the deep winter.
Comparing natural gas and electric is not an option for many people who use heat pumps. The reason they use heat pumps is that natural gas supply is not available. Their only option is through electric appliances and the heat pump is much more efficient on a yearly basis than straight electric heat.
Another subject:
As you know, I damn the use of temperature split calculations. Let me amend my position for clarification. I test and use temperature splits all the time. However, I do not report equipment deficiencies based upon these temperature splits. When you test a branch electrical circuit, you turn on the switch and see if the light comes on. If it does not come on, some of you check the light fixture for a blown out light bulb with your ticker. Based upon the presence of electrical power at the light fixture you determine whether the circuit is operating as intended (in spite of the blown out light bulb). Taking temperature splits is like turning on the light switch. If it’s there (or the light comes on) then the equipment is apparently functioning(but not necessarily correctly). However, the lack of a temperature split indicates that the unit may not be functioning or running and requires further investigation by yourself to determine if in fact it’s trying to operate or it is not operating for some other reason (a circuit breaker is turned off, a head pressure control is tripped, there is an electrical mechanical problem). Using the temperature split as a “diagnostic” of equipment “efficiency” is the issue. It cannot and should not be done. There are too many other factors that can not be evaluated through such a simple diagnostic inspection to warrant further investigation and expense to the homeowner.
Though you have been taught this in school, the use of this procedure should be limited to a system check procedure , not a diagnostic of operation/capacity.