HVAC condensation drain line connect to a plumbing vent pipe

Hi

Just wonder if this connection would pose any problem. The HVAC condensation drain line is connected to a plumbing vent stack in the attic.

256.JPG

First ask yourself what are the requirements for a condensate line .
Yes it is above cross contamination concern.{as far as liquid]

Now let me ask you is the line at the required 1/4 inch per foot ?
Does it have a trap ?
Is there an air gap?
Why are they required ?

A Plumbing vent can not terminate into a attic and with no trap would that not be the case ?

Have a pic of the other end at the unit ?
[guessing it is a horizontal unit in the attic here ]

Sheesh.

Yes it’s a problem. Sewer gases, which are deadly, now have a path back into the HVAC system ductwork. Call it out.