Dave,
We need to see the entire Section on that to fully understand it because leaving that statement as it is misleads the actual section and it’s exceptions.
**(A) Dwelling Units. **
In dwelling units, lighting outlets
shall be installed in accordance with 210.70(A)(1), (2), and
(3).
**(1) Habitable Rooms. **
At least one wall switch-controlled
lighting outlet shall be installed in every habitable room
and bathroom.
Exception No. 1: In other than kitchens and bathrooms,
one or more receptacles controlled by a wall switch shall
be permitted in lieu of lighting outlets.
Exception No. 2: Lighting outlets shall be permitted to be
controlled by occupancy sensors that are (1) in addition to
wall switches or (2) located at a customary wall switch
location and equipped with a manual override that will
allow the sensor to function as a wall switch.
**(2) Additional Locations. **
Additional lighting outlets shall
be installed in accordance with (a), (b), and ©.
(a) At least one wall switch-controlled lighting outlet
shall be installed in hallways, stairways, attached garages,
and detached garages with electric power.
(b) For dwelling units, attached garages, and detached
garages with electric power, at least one wall switch–
controlled lighting outlet shall be installed to provide illumination
on the exterior side of outdoor entrances or exits
with grade level access. A vehicle door in a garage shall not
be considered as an outdoor entrance or exit.
© Where one or more lighting outlet(s) are installed
for interior stairways, there shall be a wall switch at each
floor level, and landing level that includes an entry way, to
control the lighting outlet(s) where the stairway between
floor levels has six risers or more.
*Exception to (a), (b), and ©: In hallways, stairways, and
*
at outdoor entrances, remote, central, or automatic control
of lighting shall be permitted.
**(3) Storage or Equipment Spaces.
**
For attics, underfloor
spaces, utility rooms, and basements, at least one lighting
outlet containing a switch or controlled by a wall switch
shall be installed where these spaces are used for storage or
contain equipment requiring servicing. At least one point of
control shall be at the usual point of entry to these spaces.
The lighting outlet shall be provided at or near the equipment
requiring servicing.