Thank you, Daniel. I copy that you are saying that the grounding conductor acts as the 4th conductor if it’s routed through an EMT pipe in the ground from the sub panel to the main panel.
Jim, can an EMT pipe be a metallic raceway? Does the EMT have to be 10 feet long or the same length as a solid copper grounding rod? How long does the metallic raceway have to go?
So both panels are located on separate structures. Therefore each panel if installed under a NEC code cycle prior to 2008 can be fed with only a 3-wire feeder if no other metallic paths exist between the structures and the neutral is bonded to the cabinet. From what I can see in the photo’s there is no metal raceways involved and the 2" is PVC. Each panel is required to be connected to a GES (grounding electrode system) at each structure.
I am not sure that the 3/4" conduit going out of the bottom of the main panel in the photograph is EMT. It does appear to only have a grounding conductor going into it. What it comes down to at this point is that I need some formal in-person training about electrical panels and grounding, as I’ve already taken all the other online InterNACHI classes on electrical inspections and I’m still in need of a better understanding of how this stuff works. Thank you @rmeier2, @dhorton2 and @jmilby for your assistance.
You’re welcome! I agree, the courses still left me a little wanting, and this forum was a huge help, from people like @rmeier2
The rest of the things you learn as you go, by noticing something doesn’t look right, and asking!