Originally Posted By: lkage This post was automatically imported from our archived forum.
It appears there is a bonding strap connecting the grounded and grounding conductors to the panel running behind the main breaker. So, it appears to be okay if it’s not a sub panel.
– “I have never met a man so ignorant that I couldn’t learn something from him.”
In Canada the Neutral and the Ground even thought they are common are kept separate.
The only place they have contact is in the primary panel and then they still have their own buss.
They only have one ground conection .
All down stream panels shall go back to the primary ground.
Originally Posted By: kmcmahon This post was automatically imported from our archived forum.
I agree that if it’s the main panel, then it wouldn’t matter…of course the big question would be after all the time spent making things so pretty, why did they do it that way in the first place?
Originally Posted By: rdawes This post was automatically imported from our archived forum.
All the neutral current will run thru the small bonding screw that connects the bonding strap to the neutral bus. Granted that the neutral current is only the difference between the currents flowing in the 2 phases but it could still be considerable depending on the load distribution. The bonding strap and screw is not designed to be used as a normal current carrying conductor but only if the event that the equipment grounding conductor is needed due to a defect in a device or line.
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Quote:
408.40 Grounding of Panelboards
Panelboard cabinets and panelboard frames, if of metal, shall be in physical contact with each other and shall be grounded. Where the panelboard is used with nonmetallic raceway or cable or where separate grounding conductors are provided, a terminal bar for the grounding conductors shall be secured inside the cabinet. The terminal bar shall be bonded to the cabinet and panelboard frame, if of metal; otherwise it shall be connected to the grounding conductor that is run with the conductors feeding the panelboard.
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
In this case the main bonding jumper also becomes the neutral but it is still “hold your nose” legal.
250.24(B)(1) Routing and Sizing. This conductor shall be routed with the phase conductors and shall not be smaller than the required grounding electrode conductor
I would ask why he bothered to run a full sized neutral from the service point, then shoved it in a #4 in the last foot.
This works if you have time to explain it to him.
250.6 Objectionable Current over Grounding Conductors.
(A) Arrangement to Prevent Objectionable Current. The grounding of electrical systems, circuit conductors, surge arresters, and conductive non?current-carrying materials and equipment shall be installed and arranged in a manner that will prevent objectionable current over the grounding conductors or grounding paths.