So all three air suckers are located in the same location? Where?
Oops! Sorry Brian.
What he said…
The picture I’m starting to build is you closed up the air leakage of the house (insulation and other stuff in the report attached), added another appliance that requires more outdoor air, which was not CAZ tested (see report), and no pressure testing was done of the house with reference to the exterior to determine building pressures. I’m getting the impression that a lot of work was done to the house to go above and beyond normal house efficiency. I often find that people think that if a little is good, a lot will be better. I am not convinced you are aware of what is actually going on right now after all this work. If you are, you’re not providing the information we need here. The HRV should help equalize building pressures that were created from all the other work you had done, specifically that insulation in the attic perception.
The picture of the HRV you posted with arrows, shows perceived airflow directions. The HRV transfers heat through counterflow duct design.
Your pic shows parallel air flow?
When we fix things, we look at a specific problem to correct. You’re coming at this from all directions. What is the specific problem? Air pressure? What is the building air pressure?
Building efficiency, air quality, health issues, appliance operation, comfort? You talked about them all.
Which single one is the problem. All the other stuff are issues because of the problem.
You need to test for that one problem. Don’t be tunnel visioned with that insulation thing. Several people here can’t perceive that as being the problem you describe.
You are also hug on “stack effect” as being the cause of pressure differential. Well, you have not convinced me or others that is the case. What do you have to document that?
If you don’t have anything, get someone in there with a micro-manometer and test pressures with all the scenarios under normal use of the house. Test with one system operating at a time.
You mentioned appliance back draft only one time? Your report said there are no appliances to test for CAZ?
Woodstove also in the full finished basement.
More bits and pieces come to light…