Ok,
I sited this on an inspection, the owner called an electrician, was charged $70 for the visit, and the electrician stated there was no violations in the main panel and left. Does the Florida code specifically state one neutral to a lug? I’ve seen this a lot on houses less than five years old.
Jeff,
Thanks for your reply. I am not in code inforcement nor did I call this a violation. I pointed it out as a hazard with the typical verbage. I clearly see two neutrals on one lug. Are you saying I was wrong to spot it as an issue?
Rick
The wording in your report can make you look like you’re a competent inspector, or it can make you look like a “fool” in the eyes of the home owner and the contractors that might be involved.
Something along these lines would have been appropriate based on a 10 year old installation;
Current standards allow for only one neutral to terminate under the individual lugs of the terminal bar. Although this may have been an acceptable practice at the time the panel was installed, we recommend that the neutrals be separated and terminated in a manner consistent with the most current safety standards.
Thanks David,
But the issue is, the electrician he called said, “the box is fine there are no violations–the wiring is fine.” Would another electrician identify the issue and fix it? Should I have sited it as an issue and then leave it alone and give them the move in certified approval? Its not the owner won’t fix it; he believes the electrician didn’t see any reason to change the wiring.
Rick I don’t know how you handle your move in certified program so don’t intend to try to tell you what to do; but as Jeff pointed out, this is an issue of today’s standards versus those of yesteryear.
Can you just put in there that this is a condition that is no longer acceptable in today’s standards, however the current homeowner is not required to make any upgrades until service is changed.
You are advising everyone of the condition that continues to exist.
Get a copy of the state disclosure requirements from where you live (the real estate agents have them). These things normally set the tone by which you should be reporting by.
If you are inspecting a house built in 1901, is it a deficiency not to have two dedicated circuits that are GFCI protected the kitchen?
No. However when someone starts plugging in extension cords all over the place it does become a hazard.
You’re not certifying the home to be up to current building standards.
You are helping the seller “disclose”. The seller is not required to fix anything, simply disclose it.
The neutral wires are grouped together inside the panel at the neutral buss bar. All wires should terminate into individual set screws by today’s standards.This was more than likely not a requirement at the time of construction, but is a updated safety requirement and should be repaired if you choose to. A qualified electrician should always perform this repair.
More than likely it was required at the time of construction also. Someone failed to read the panel label. This is why the requirement was added to the NEC as too many were not aware of the listing and labeling requirements that were already in place.
It was sufficent for the time it was installed, and complied with the AHJ. Its not a repair. Its only a recommendation to update it. Are you going to request they rewire a 2 strand romex because it doesn’t meet todays standards?