Originally Posted By: gsutterfield This post was automatically imported from our archived forum.
Joe
Assuming that is 12-3 or 14-3 how in the hell did they get the wire nuts on and close up the box ??? At least they didn't hide it under the insulation ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)
Originally Posted By: gsutterfield This post was automatically imported from our archived forum.
Joe
I mentioned wirenuts [ wire connectors ] because it was obvious from the picture care was not one of his priorities ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)
Originally Posted By: rpalac This post was automatically imported from our archived forum.
WoW… How did they manage to get the cover on?
NEC Article 314.16 Number of conductors in Outlet,Device and Junction Boxes.
Boxes and conduits bodies shall be of sufficient size to provide free space for all enclosed conductors. In no case shall the volume of the box as calculated in 314.16(a), be less than the fill calculation as calculated in 314.16(b).....................
the table which shows the different box dimensions is very clear:
(this is a 4x4x1-1/4 box) maximum conductors
#14 wire (9) the grounds are counted as one conductor(314.16(b-5).
#12 wire (![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif) " " " " "
since one box has 11 wires and the other 8 that I can see....there's not a chance
Also the fact as was pointed out that the wires need to be fastened within 12" of the box and at increments as in Article 320.23(In accessible Attic), 334.23(In Accessible Attic), 334.30(Securing and Supporting), and 330.4(d) (joist penetrations)
One over site that comes to mind even if you had a larger box or extension ring very often the wires are not left long enough by code to work on. They must be six inches longer then the face edge of the box. Article 300.14 ( Length of Free Conductors)
All that said, technical or not even if it were in a 12x12x12 can this probably would be improper because it is more than likely one circuit maybe two and the load calculation is probably way out of kilter. (Article 210)
That's my back ground.
Great picture!
So what did you do as a reply for the inspection......?
Bob
Originally Posted By: JIM WALKER This post was automatically imported from our archived forum.
Mike i would have left that company real fast too.I just love it when a guy says im only over by — wires.I then ask him what it will cost us to fix it if the inspectors catches it, and inspectors are sharp at this.