Originally Posted By: jlybolt This post was automatically imported from our archived forum.
Inspected a home that had outlet covers missing at several locations.
Decided to take a look inside and found the receptacles grounds pigtailed together. Some outlets had up to 5
#12 gauge wire nutted together.
This seems excessive. The receptacles even seemed to be pushed out from the box because of the wiring. Any comments would be appreciated.
thanks
system
(system)
July 18, 2005, 12:00am
2
Originally Posted By: bsumpter This post was automatically imported from our archived forum.
According to the 2002 NEC it could be:
314.16B 18cu.in. box too small for 3 12/2 Romex
314.16B1 Number and size of conductors exiting box
Either way, an overstuffed box is a no-go according to code check
It makes you wonder what else went on in the branch wiring....and elsewhere for that matter!
Are you going to call it out?
-- "In the fields of observation, chance favors only the mind that is prepared"
Louis Pasteur
system
(system)
July 18, 2005, 12:00am
3
Originally Posted By: mboyett This post was automatically imported from our archived forum.
http://www.taunton.com/finehomebuilding/pages/h00134.asp – Mike Boyett
Capital City Inspections
Austin, Tx
www.capcityinspections.com
system
(system)
July 18, 2005, 12:00am
4
Originally Posted By: jlybolt This post was automatically imported from our archived forum.
I really appreciate the help. I am definetely going to call it out as see licensed electrician with some other electrical problems found. Thanks
system
(system)
July 24, 2005, 12:00am
5
Originally Posted By: jmyers This post was automatically imported from our archived forum.
James,
If those are Carlon brand plastic boxes, I do believe they place a reference in the back of the box as to how many, of what size wires it is allowed to use according to the NEC.
-- Joe Myers
A & N Inspections, Inc.
http://anii.biz