Plumbing identification

Don’t believe I’ve seen one of these before. Looks like some sort of bleed valve. Found it ‘Teed’ into a water heater inlet line today?

1 Like

Almost looks like a vacuum relief valve missing its cap.

https://manualzz.com/doc/59345942/cash-acme-22397lf-brass-1-2-in-mnpt-vacuum-relief-valve-m

9 Likes

Good research Ryan! :wink: :+1:

1 Like

If I had to guess the water heater may have been installed in an attic or upper floor. That is the only place an atmospheric vacuum breaker would be needed.

Used when a pressurized vessel is located above the potable water piping.

4 Likes

2018 IPC 504.2 Vacuum Relief Valve:

Bottom fed water heaters and bottom fed tanks connected to water heaters shall have a vacuum relief valve installed. The vacuum relief valve shall comply with ANSI Z21.22.

https://codes.iccsafe.org/content/IPC2018/chapter-5-water-heaters#IPC2018_Ch05_Sec504.2

Here is a UPC diagram

https://forms.iapmo.org/email_marketing/codespotlight/2018/june28.htm

Here is a good explanation of why these are used.

I’m seeing these a lot on new construction homes that use a heat pump water heater with a bottom feed cold inlet.

4 Likes

All good information, Thanks guys. Curious thing is the water heater is top fed and located on the ground floor (slab on grade).
confused-animated-smiley

It is a requirement in some states, like Massachusetts, regardless of tank’s location.

1 Like

Could be a County Regulation. I don’t normally do inspections in this county.
confused-animated-smiley