Pool bonding question
2015 IRC E4204.2 refers to bonding together of different elements related to swimming pools but bonding isn’t required to connect to a remote panelboard, service equipment, or electrode. Is this because one or more of the elements required to be bonded will act as an electrode?
I thought that if voltage got onto any conductive elements, that bonding together of multiple elements plus their connection to ground would reduce the potential for shock/electrocution. If there’s no connection to ground, doesn’t that just energize everything bonded together?
If all those things bonded together are energized, how does that make things safe? If one of them becomes energized, now they all are. If they’re bonded and connected to a breaker and also grounded then the breaker is likely to trip, but if they don’t have to be connected to a panel or electrode, how are they all protected?
Bonded to earth ground.
The pool equipment is bonded to the panel via the EGC run with the branch circuit to the pump. All of the metal parts are bonded together via the equipotential bonding conductor that also connects to the pump. That is why you do not need to run a bonding jumper all the way back to the panel.
Got it, thanks Robert! I still don’t understand that perimeter surface bonding within 3’ of the pool edge though.
i have always relied on hands-on or diagrams to compensate my reading diability
don’t know of this will help
2017 NEC 680.pdf (8.4 MB)
Check this out…
“The purpose of bonding is to connect metal parts together so that if one part becomes electrically energized its voltage will not be different from any nearby metal part. If metal parts are at different voltages, a person touching one part could become the electrical path to ground if he touches a nearby metal part. Bonding and grounding are not the same. Bonding connects metal parts to each other. Grounding connects electrical equipment to an earth grounding point. Note that some metal parts, such as pool circulation equipment, must be both grounded and bonded. In this case, the grounding wire is usually contained in the electrical wires serving the equipment and the bonding wire is usually connected to the metal exterior of the equipment.”
Bonding of Metal Near Swimming Pools and Spas.docx (12.9 KB)
To add to what Roy posted above.
What is electrical potential?
To understand potential, imagine how water flows through a pipe. It will naturally flow from an area of higher pressure to an area of lower pressure. If both ends of the pipe have equal pressure the water will not move, regardless of the level of pressure.
Electricity works in the same way. There has to be a difference in pressure (or voltage) to create a flow of electricity from one point to another.
The purpose of equipotential bonding is to equalize the pressure around the entire pool so your body doesn’t create the circuit between areas of differing potential which would result in getting shocked.
This is done by creating a “bonding grid.”
Similar to this lineman technique.
Barehand or Potential
The barehanded approach has a live line worker performing the work in direct electric contact with live parts. Before contact, the worker’s body is raised to the same electric potential as the live parts, and then held there by electric connection, while maintaining suitable isolation from the surroundings which are at different potentials, like the ground, other people or trees. Because the worker and the work are at the same potential, no current flows through the worker.
Big, big help Barry, thanks! The illustrations do make it easier to understand.
May sound stupid but, does a brass hose bibb near the pool need to be bonded if all the plumbing is cpvc?
Is the hose bib within 5’ of the pool?
Yes it is. I was just wondering since the plumbing is plastic.
As silly as it sounds that would fall under a fixed metal part {NEC 680.26(B)(7)} and when within 5’ of the pool it would require bonding.
If all the plumbing up to the brass hose bib is PVC, what do you bond or ground the hose bib to?
You would bond it the equipotential bonding grid around the pool.
That was what I was thinking but thought possibly the plastic plumbing would make a difference. Thanks.
It’s silly for such a small piece of metal but the NEC doesn’t have an exception for small fixed metal parts. Funny thing is for metal fittings that are not over 4" and penetrate into the pool structure by 1" or less bonding would not be required. {680.26(B)(5)}