Sorry to bring up an old thread, I came across this while trying to research measurement errors from the ideal suretest and I wanted to bring some information I found from my testing to the forum.
The way the suretest measures voltage drop may hide some problems with your utility service conductors. In my case it appeared there was a high voltage drop in most my outlets 10-13% @ 15A using the sure test. The sure test showed high impedance on only the hot conductor but fine on the neutral and ground. So I started checking splices in the outlet boxes and didn’t find much or get any improvement changing old wire nuts out.
The issue in my case was the way the suretest calculates neutral impedance. It takes a voltage measurement N to G unloaded and then N-G loaded, since the neutral is bonded to ground at panel it doesn’t know what is going on before that connection. If you have a high impedance neutral connection from the utility, in my case about 0.5ohms, the suretest just sees that as part of the total voltage drop and it is added to the Line/hot conductors impedance, misleading me to believe there was problems inside the house wiring but half of the voltage drop was coming from the neutral service wiring.
Long story short the utility placed a temporary conductor in place from the transformer to my main panel until they get someone out to run a proper neutral wire to my panel.
At least either way the suretest did lead me to test more to find the source of the problem, in my case a bad neutral which caused voltage imbalance at the main panel of up to around 10VAC with typical loads.