Originally Posted By: rcooke This post was automatically imported from our archived forum.
Looks to me like the service stack is What we in Canada Call thin wall conduit with rain tight conectors . This is not allowed in Ontario. We are allowed to use Plastic or thread pipe. Are you allowed to use
Thinwall ( EMT ) in all states . Thanks Roy Cooke sr.
Originally Posted By: roconnor This post was automatically imported from our archived forum.
bbadger wrote:
Yes the use of EMT for service risers is allowed.
True ... as long as there are raintight fittings (NEC 358.42) and it is not subject to "severe physical damage", like next to a driveway (NEC 358.12.1)
Also note that IRC Table 3701.4 lists EMT as acceptable where "Run exposed", but would not be acceptable where "Run exposed and subject to physical damage" ... hmmmmm ... would exposed EMT service conduit be "subject to physical damage" from a falling tree or flying debris is a storm ... ![icon_eek.gif](upload://yuxgmvDDEGIQPAyP9sRnK0D0CCY.gif)
-- Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong