Originally Posted By: jhagarty This post was automatically imported from our archived forum.
Plugged the Tester in and all three lights lit.
Thinking it was a Bad Tester, I plugged another Tester into the receptacle.
Hmmm...
-- Joseph Hagarty
HouseMaster / Main Line, PA
joseph.hagarty@housemaster.com
www.householdinspector.com
Phone: 610-399-9864
Fax : 610-399-9865
HouseMaster. Home inspections. Done right.
system
(system)
May 26, 2005, 12:00am
2
Originally Posted By: jpope This post was automatically imported from our archived forum.
I’ve never seen that. Do you not have a SureTest?
– Jeff Pope
JPI Home Inspection Service
“At JPI, we’ll help you look better”
(661) 212-0738
system
(system)
May 26, 2005, 12:00am
3
Originally Posted By: hgordon This post was automatically imported from our archived forum.
Hmmm…I have but it blew my SureTest Up.
– Harvey Gordon
SE Florida NACHI Chapter - President
hgordon@fl.nachi.org
system
(system)
May 26, 2005, 12:00am
4
Originally Posted By: jpope This post was automatically imported from our archived forum.
I lost a SureTest when one of these was wired for 240v. Maybe this is the same?
– Jeff Pope
JPI Home Inspection Service
“At JPI, we’ll help you look better”
(661) 212-0738
system
(system)
May 26, 2005, 12:00am
5
Originally Posted By: hgordon This post was automatically imported from our archived forum.
Hmmm…
– Harvey Gordon
SE Florida NACHI Chapter - President
hgordon@fl.nachi.org
system
(system)
May 26, 2005, 12:00am
6
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
I bet there is 240v in that plug. A 3 light tester just looks at the 3 pins as a delta. The only way I can think that you get all 3 lights is if both hot and “neutral” have voltage on them (ref ground) and they are out of phase. The hot/neutral light is the bright one, seeing 240v. The 2 to ground see 120v.
I am surprised this would blow a suretest. It never hurt my Ecos, in fact that is one of the documented results.
system
(system)
May 26, 2005, 12:00am
7
Originally Posted By: jwilliams4 This post was automatically imported from our archived forum.
Time to get the ol’ Amprobe!
– “not just an inspection, but an education”
system
(system)
May 27, 2005, 12:00am
8
Originally Posted By: apightling This post was automatically imported from our archived forum.
Yep, 240 is the only non fault situation that would cause this. I suppose you could have some wildly convoluted fault with hot shorted to neutral, an incorrect neutral breaker blown and a bad ground . . . too wierd . . 'gotta be 240 wired.
-ap
system
(system)
May 27, 2005, 12:00am
9
Originally Posted By: rbennett This post was automatically imported from our archived forum.
are out of phase???
Someone help
RLB
system
(system)
May 27, 2005, 12:00am
10
Originally Posted By: dbowers This post was automatically imported from our archived forum.
When you checked the outlet with your volts/ohm meter what did it say??
system
(system)
May 27, 2005, 12:00am
11
Originally Posted By: jhagarty This post was automatically imported from our archived forum.
Dan:
Did not check it for amps or voltage.
This was only a single representative sampling of the electrical problems in this 80-90 year old home.
Report called for a total rewiring of the home.
-- Joseph Hagarty
HouseMaster / Main Line, PA
joseph.hagarty@housemaster.com
www.householdinspector.com
Phone: 610-399-9864
Fax : 610-399-9865
HouseMaster. Home inspections. Done right.
system
(system)
May 27, 2005, 12:00am
12
Originally Posted By: apightling This post was automatically imported from our archived forum.
I would flag that one as a dangerous condition and advise the client to get an electrician involved asap.
-ap