jfrederick
(Joshua Frederick)
February 2, 2016, 2:46pm
1
I know a best practice is no more than 1/4" - 1" of sheathing inside the panel, but why? I thought I’ve read something about excess heat, is that true?
I know it’s sloppy and a tad “overcrowded,” but there is nothing in the NEC where this is unacceptable, correct?
Thanks in advance.
lkage
(Larry Kage, CMI)
February 2, 2016, 2:49pm
2
jfrederick:
I know a best practice is no more than 1/4" - 1" of sheathing inside the panel, but why? I thought I’ve read something about excess heat, is that true?
I know it’s sloppy and a tad “overcrowded,” but there is nothing in the NEC where this is unacceptable, correct?
Thanks in advance.
Correct as far as the sheathing but coming through a knockout without a connector needs attention.
Jim_Port
(Jim Port)
February 2, 2016, 3:36pm
3
The NEC requires at least 1/4" inside the box. As long as there is at least 6" of free conductor outside the sheath it will meet code.
lkage
(Larry Kage, CMI)
February 2, 2016, 5:06pm
4
Thanks, Jim. Good information.
gkeene
(Greg Keene, CMI)
February 3, 2016, 1:16am
5
Thanks Jim. Love to learn new stuff. thought it was more than that (6in.)