Rooftop unit

Originally Posted By: rray
This post was automatically imported from our archived forum.



Here’s my first ever rooftop unit. Do I like the condensate drain going into the VTR? If not, why not?


http://www.nachi.org/bbsystem/usrimages/fauDrain1.jpg
http://www.nachi.org/bbsystem/usrimages/fauDrain.jpg

![icon_twisted.gif](upload://xjO326gspdTNE5QS3UTl0a0Rtvy.gif)


--
Home inspections. . . .
One home at a time.

Originally Posted By: tallen
This post was automatically imported from our archived forum.



I have seen it done that way a few times.


The Code requires that the condensate lines terminate outside the building above the finish grade, and they must be trapped.

Why? hmmm, I don't remember. Must be time for bed. Maybe so you can tell when it's clogged ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)


--
I have put the past behind me,
where , however, it now sits, making rude remarks.

www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Must be trapped and must be through an air gap, but, more importantly, that now becomes a wet vent, and it was not likely designed as a wet vent.


I believe I am using that terminology correctly, wet vents are not my strong suit.


--
Jerry Peck
South Florida

Originally Posted By: tallen
This post was automatically imported from our archived forum.



That’s the ticket Jerry icon_smile.gif


It is the same with evap coolers they must have an overflow drain that extends off the roof(building) or into a gutter system. So that it is keeping the dry vent dry as it was designed.

Thanks Jerry


--
I have put the past behind me,
where , however, it now sits, making rude remarks.

www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: cbottger
This post was automatically imported from our archived forum.



This unit appears to be a what is referred to as a Gas Pac do I see a gas


line traveling across the roof to this unit?? Most package combo units have the blower set up to blow across the refrigerant coil rather than drawing (sucking for lack of a better word) this would be applying a positive pressure on the condensate drain up to the P-trap and would be loosing conditioned air thru the cleanout Tee that is closet to the unit. This could be determined by simply placing your hand over the vertical open Tee and if a riser coming out of the top of the Tee was installed with a non-glued cap to prevent air loss during the cooling season does not help in the heating season when the trap goes dry even though there is a second Tee after the P-trap I would have been concerned that pressure was being discharged into the top of the plumbing vent. Perhaps bubbles in the commode. (Joke) of course. As a general rule stay away from plumbing vents with condensate drains unless the furnace is (90%) or better and produces condensate into this line in the heating season.



Don’t argue with an idiot someone watching may not be able to tell the difference.

Originally Posted By: Blaine Wiley
This post was automatically imported from our archived forum.



Looks like the roof has seen better days too icon_biggrin.gif


Originally Posted By: rray
This post was automatically imported from our archived forum.



Come on, Blaine. Cut me some slack. That was the good side of the house (north). Here’s the south side roof:


http://www.nachi.org/bbsystem/usrimages/roof1.jpg

By the way, I don't walk roofs, yet that is an interesting angle down to the roof that I got there! LOL ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)




--