Service Grounding

I have a GE 1/2" format 150mp. main breaker panel. What appears to be the main grounding conductor is a #2 alum. conductor to a water pipe connection, There is also a #6 connection to a single driven rod outside.

The problem is the water service tubing is plastic, which in my opinion makes the water pipe connection merely a bonding connection for the water piping. You can see the outline of a hose clamp in one photo, which tells me the main is plastic. Is the #6 to the rod a sufficient grounding conductor by itself? My first inclination is no. The driven rod looks like a 1/2" copper plated rod also.

I also did mention the double tapped neutrals.

DSC01135.JPG

DSC01136.JPG

If there is no water pipe electrode a rod electrode is all that’s required. Now two rods are required unless you can prove that one rod has a resistance of 25 ohms or less. The largest GEC required to a ground rod is #6 Cu regardless of the service entrance conductor size, unless subject to physical damage then the largest required is a #4 Cu.