Square D main panel and Cutler Hammer sub panel

If this is the service then there are few things besides those already mentioned. There is no GEC connection and no main bonding jumper. Not sure how all of those cable enter through one KO in the top.

Also depending on what the 50 amp CB is feeding those conductors appear to be #8 which is only good for 40 amps if it’s NM cable.