Sq D 200 amp panel with Cutler Hammer Breaker

Hi. Needed a quick answer, if anyone has one!

Can Cutler Hammer breakers usually be crossed over and installed in Square D panel? As best as I could read the CH label - Type C L 720, T060429, CU/AL SWD

Thanks,

This all gets down to how you regard “classified breakers”. U/L and C/H say they are OK. SqD doesn’t

Classified Breaker Compatibility Chart](http://www.eaton.com/ecm/idcplg?IdcService=GET_FILE&allowInterrupt=1&RevisionSelectionMethod=LatestReleased&Rendition=Primary&&dDocName=1046632560357)
Native Document | 5651B63SH04.PDF | (340KB) | relevance:84.99 %
Eaton’s Cutler-Hammer Type CL Breakers list for UL approved replacements in Crouse Hinds, GE, ITE, Siemens, Square D Homeline and Murray loadcenters.
"

http://www.eaton.com/ecm/idcplg?IdcService=GET_FILE&allowInterrupt=1&RevisionSelectionMethod=LatestReleased&Rendition=Primary&&dDocName=1046632560357

Square D’s side
http://ecatalog.squared.com/techlib/docdetail.cfm?oid=0900892680139d70

Inspectors split on the issue, most side with U/L listing

of course square d isn’t going to say its ok. That would be like coca-cola saying “you can buy our bottles but you can refill them with pepsi if you want to” Go with the UL recommendation…unbiased.

Doesn’t the NEC always refer to the manufacturer’s instructions, i.e. panel label?

No, it says to go with listing and labeling instructions. Listing is from UL, and the UL mandates the required labeling language. “Labeling” is not manufacturer’s instructions. Labeling is done in compliance with the UL Marking Guide.

Blaine
That is why Eaton C/H will give you a sticker to put in the panel stating the U/L classification of their replacement breaker. It is clear that SqD will not evaluate a C/H breaker in their panel so you have the U/L blessing from their evaluation.

Thanks for all the info.