I’ve run across a Square D QO series panel with some double-lugged breakers. It appears to have the proper screw plate with the two channels that allows it to be safely double tapped. However, I can’t find any labels that say “1 or 2 conductors…”.
Strictly speaking, the code says a double tap is OK only if there is manufacturer labeling. Does this mean I ought to call this out, even though it seems to be the type that it’s OK to double tap?
Type QO breakers are listed for one or two conductors within a certain range. You can find this on the Square D website. Also if you access to a CB you can see the diagram on the side of the breaker.
Thanks everyone very much. I wasn’t aware of the listing ranges. That’s going to be very helpful, since those labels are sometimes almost impossible to read.
Yes, exactly Larry. It seems there isn’t always a label, but that pressure plate is what mechanically enables the safe double tap, so that is what really matters I would think.