Originally Posted By: lkage This post was automatically imported from our archived forum.
senomoto wrote:
Two wires being pigtailed and then tapped into one circuit breaker. This is not standard installation and the question is "is this still considered a double tap?
No, I don't believe it would be considered a double tap. The wires look the same size (#12 for the 20 amp breaker).
Are the yellow breakers AFCI's?
-- "I have never met a man so ignorant that I couldn't learn something from him."
Galileo Galilei
Originally Posted By: James D Mosier This post was automatically imported from our archived forum.
I don’t consider the two wire-nutted wires a double tap, there’s only one wire at the breaker, it’s really no different than if they were wire-nutted in the first junction box and then went their separate ways. Wire nuts are definately allowed in old work.
I don't think the ground crossing the main lugs is "wrong" but it could have been done better.
Let's see what the pros have to say.
Not impying that Larry isn't a pro, I started my post before he posted.
Originally Posted By: jmyers This post was automatically imported from our archived forum.
I have two questions. First would be…did you take that picture sideways?, or is the panel installed sideways?
That would be a code violation for that panel if indeed it is installed sideways.
Second would be....is the splice in the panel? If I am not mistaken, panels are not allowed to be used as a junction box, so that could be considered a code violation.
Originally Posted By: Joey D’Adamo This post was automatically imported from our archived forum.
By that they generally mean that wires should not enter and then leave only being spliced to each other and not a peice of equipment within the panel. If it is spliced to a peice of equipment within the panel, it is considered acceptable. This was the explanation given here once before but I can't remember who it was from.
Originally Posted By: dbush This post was automatically imported from our archived forum.
Joe, the code is rather vague. It actually says “it can be used as a junction, provided there is reasonable room to do so” or some ambigious crap like that.
dbush wrote:
Joe, the code is rather vague. It actually says "it can be used as a junction, provided there is reasonable room to do so" or some ambigious crap like that.
Now that you mention it, I seem to remember either Joe T or Greg F talking a lot about box fill when it came to this topic. I suppose one of them will weigh in soon and offer the explanation again.
Connecting two wires in the panel before running a single wire to to breaker is permitted if there is enough space (appears to be plenty), and if it’s a solidly connected and approved splice device (e.g. special wire nuts for AL-CU connections).
There is the possibility of nuisance trips from two circuits connected to one breaker depending on how heavily the two pigtailed circuit wires are which you should warn your clients about.
JMO and 2-nickels ...
-- Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Quote:
312.7 Space in Enclosures.
Cabinets and cutout boxes shall have sufficient space to accommodate all conductors installed in them without crowding.
312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided.
The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
Originally Posted By: lgoodman This post was automatically imported from our archived forum.
There exists a possibility of trips on any circuit depending on how heavily it used. I hesitate to call them nuisance trips because they are responding to amperage in excess of the wires ampacity. If you report this one you might as well report the possibility of trips on all the breakers in the panel unless you know that this one presents a special problem.
If I recognized a problem I would report it but it is just as possible that this splice was put here because it was the least utilized circuit in the panel. That is how a thinking electrician would pick the circuit to tap.
I think you will just be filling your report with something that seems negative but actually is of no real import to the buyer's decision.
jmyers wrote:
Joe T,
In your opinion, would that pigtail in the panel qualify as using the panel as a junction box?
Joe
Yes, however, that single lonely innocent splice will not create a serious and life threatening problem.
The rule I quoted above allows quite a few more, and if we calculated the number of wires permitted to pass through tha cabinet, using it as a raceway, we would be amazed.
jtedesco wrote:
jmyers wrote:
Joe T,
Joe
A 40% fill is not to be exceeded.
Really appreciate your answer Joe T. It helps having your opinion as well as the code quotes.
Thanks.
Galileo Galilei
I dont agree.
A single wire correctly sized on a single breaker usually works fine, unless it's not designed correctly. But with two wires to a single breaker (say two #12 on a 20A breaker ... which is up to about 50A using typical 60C NM wire, or 60A using 90C THHN wire) either with a pigtail or a breaker listed for two wires (e.g. SQD QO) the likelihood of nuisance trips increases dramatically. Also, many times this is done with a panel that is undersized to begin with, with a lack of breaker spaces, which just adds salt to the wound.
Not alerting your client to the fact that there could be nuisance trips if the two circuits connected to the single breaker are heavily loaded, or that it might be an indication of an overloaded panel if it was done because there were no more breaker spaces, would be poor practice for an HI in my opinion.
Eagle Engineering ?