Need some help with understair protection. Correct me if I am wrong but there should be fireblocking below this stairway (see pictures).The open space is the floor joist area for the second floor. Better yet, I was under the impression if you were able to access the bottom of the stairway the walls and ceiling should be sheetrocked with 1/2" rock?
**R314.8 Under stair protection. **Enclosed accessible space under
stairs shall have walls, under stair surface and any soffits protected
on the enclosed side with 1/2-inch (12.7 mm) gypsum
board.
**
Would there be any exceptions to this rule? For example, if the underside of the stairwell is accessible thru the garage. I cant find anything that this would be allowed.
It was accessible thru the garage and the the door into the stairwell was not rated. I did note the door and defer this area for further evaluation. Thanks
Why recommend drywalling over what appears to be improper framing and attachment of the stringer? Is the stair improperly attached? In my opinion drywalling is the secondary concern. Why recommend covering a framing issue with firewall under the guise of fire rating, you cannot omit one problem over that of another, or am I missing something?
Based solely on the photos the joist should be doubled where the stringer attached. The large gap in the framing at this area, again as evidenced by the photo does not relay that it is properly framed. I can’t recall ever seeing framing like this in new construction.
I don’t see “true” stringers at all.
What I do see is a 2X2 cleat running beneath something that looks like drywall with some plywood cleats nailed to it’s face presumably to carry the treads.
That’s just plain wrong.
And I would definately run a third stringer in the center ,no matter how long the tread, if I were using plywood as treads.