210.4 Multiwire Branch Circuits. (B) Disconnecting Means. Each multiwire branch circuit must have a means to simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
[RIGHT][RIGHT]
As Michael mentioned the MWBC contains two ungrounded and one grounded conductor (neutral) which is a shared between the two ungrounded conductors. A MWBC can be either 2 or 3 ungrounded with one grounded conductor. The 3 ungrounded/1 grounded MWBC would be from a 3Ø system. It’s ungrounded because it’s not intentionally connected to ground and has a voltage potential to ground.
Yes. A standard 120 volt circuit will consist of one ungrounded conductor (hot), one grounded conductor (neutral) and one equipment grounding conductor (ground). A MWBC will contain one additional ungrounded conductor (hot).
A standard 240 volt circuit will contain two ungrounded conductors (hots) and an equipment grounding conductor (ground). Depending on the type of circuit and the code in effect, the 240V circuit may also contain one grounded conductor (neutral).
Yep, and never crossed my mind that a hot wire was an ungrounded conductor. I always looked at it a a hot wire period.
Glad I was a builder and not an electrician. :)
Side question…In this configuration, wouldn’t the neutral/grounded conductor get overloaded serving as the return circuit for both 120 circuits instead of the common 220 configuration?
Boy, I am glad I got Mike Holt and a bunch of friends on this network so I can help someone else. :mrgreen:
*Caution: If the ungrounded conductors of a multiwire circuit aren’t terminated to different phases or lines, the currents on the neutral conductor won’t cancel, but will add, which can cause an overload on the neutral conductor. *