Originally Posted By: Rafael
This post was automatically imported from our archived forum.



ok, gotta another one here , this house use well not public wate. is this the reason for so many pipes connected to the water heater.


[ Image: http://www.nachi.org/bbsystem/usrimages/1/100_1819.JPG ]


Originally Posted By: bking
This post was automatically imported from our archived forum.



I don’t think a well is the reason. Looks like some sort of winter / summer changeover. There must be some more to this in the attic and maybe a recirculation pump too on that timer box.


What is the device on the upper hot to cold crossover pipe?


--
www.BAKingHomeInspections.com

Originally Posted By: Rafael
This post was automatically imported from our archived forum.



there is a solar water heater on the roof is what i am told it is if that helps,thanks


Originally Posted By: away
This post was automatically imported from our archived forum.



Rafael,


Here is my guess on the situation. BTW adding that comment about the solar system clarified it for me.

The water comes in through the wall on the right, goes up the pipe on the right to the solar system. The lower valve on the right is closed to prevent water from getting to the gas WH.

After circulating through the solar system it comes back down the pipe on the left, goes through the little insulated jog in the middle to the cold water line to the gas WH. The valve on the left is closed to prevent it from going into the hot water line on the gas WH.

The water is then heated further, if needed, in the gas WH and exits normally via the hot water line.

It looks like the solar system is used to preheat the water so the gas WH doesn't have to work as hard or as long. There may also be a recirc pump as mentioned so the gas WH doesn't have to keep the storage tank hot as the solar system will do that.

The upper right valve is to isolate the solar system. Close that and water will crossover the upper bare copper then back down to the gas WH and things will be just like a "regular" setup. Well except you will have all those joints and valves that can potentially leak.


--
Andrew Way
Keystone Residential Inspection Services PLLC
817.441.9598
www.keystoneinspections.com

Originally Posted By: Monte Lunde
This post was automatically imported from our archived forum.



Looks like the TPRV pipe will have a threaded end also, if it does a No No.



Monte Lunde CCI, CCPM, CRI


Viking Construction Services Inc.

Originally Posted By: Rafael
This post was automatically imported from our archived forum.



thanks all, i appreciate your input on this.


Originally Posted By: Rafael
This post was automatically imported from our archived forum.



TPRV pipe is galv and have a threaded end . is this a code violation. should this be copper?


Originally Posted By: Monte Lunde
This post was automatically imported from our archived forum.



No threaded end (IRC 2803.6.1, UPC 608.5)


Galvanized steel OK (IRC 2803.6.1, UPC 608.5)


If it was threaded then someone could cap the pipe and that would defeat the purpose of the TPRV


--
Monte Lunde CCI, CCPM, CRI
Viking Construction Services Inc.

Originally Posted By: Rafael
This post was automatically imported from our archived forum.



thanks Monte