Floor joists are 12" wood I-joist, I know the manufacturer installs knock-outs for running tubing etc. The plumber drilled 2-1/2" to 3" holes about 1 foot from the carrying beam end and top of beam center. Does anybody know if this creates a structural concern or not?
go to manufactuers web site for the joists, they always show an allowable cut / hole drilling diagram or instructions. Normaly new or larger holes are allowed near the ends or within a few feet of the end.
Hi Ron
I think you’ve got it backwards. The maximum shear stress occurs at the ends (support) so the further away from the end, the larger the allowed hole.