Originally Posted By: dedwards This post was automatically imported from our archived forum.
Same people that write the NEC put this out. It is only about 5 pages long and that includes the Table of Contents and Index. About as straighforward as you can get and it lays everything a HI needs to know and stay inside the guidelines of the SOP. Comes at inspections from the “Safety” angle and doesn’t get bogged down with chapter and verse like NEC does. Costs about 35 dollars but you can order it online or go to www.constructionbook.com
Whoops, wait a minute, that website no longer has them but go the NFPA's website and order it. Sorry, I got mine some time ago from the other source.
-- Raymond Wand
Alton, ON
The value of experience is not in seeing much,
but in seeing wisely. - Sir William Osler 1905
NACHI Member
Registered Home Inspector (OAHI)
http://www.raymondwand.ca
I belive that is a lightning surge suppresser. . .
And I believe that the manufacturers installation instructions allow for that type of connection
-- Jeff Pope
JPI Home Inspection Service
(661) 212-0738
Originally Posted By: tallen This post was automatically imported from our archived forum.
Jeff, I think they actually recommend that they be installed at the mains.
And it's allowed by the NEC
230-82 exception 4
-- I have put the past behind me,
where , however, it now sits, making rude remarks.
Originally Posted By: fbartlo This post was automatically imported from our archived forum.
might there be?
A properly operating breaker would trip if overloaded, after all. In my reports, I've always told the client that a double tap would be likely to trip the breaker or blow the fuse often.
Originally Posted By: rwand1 This post was automatically imported from our archived forum.
Thanks guys!
Regards
-- Raymond Wand
Alton, ON
NACHI Member
I think that picture is of the main
230-82 exception 4
Actually, NEC230.82 requires the equipment to be connected to the supply side of the service disconnect. Raymond's picture shows a suppressor that is clearly connected at the load side.
The method of connection is not addressed by the NEC directly at this point.
Now what?
P.S.
FYI Todd - it's a rule, not an exception, and it's (3) not (4).
Only an over load would cause the breaker to trip - whether a double tap is present or not.
-- Jeff Pope
(661) 212-0738
Yes, of course. And a double tap generally implies a greater load on the fuse or breaker than originally intended, and would be the one I'd bet would overload most often. Obviously it still depends upon how much the individual circuits are carrying.
I had one rental that had the furnace, basement, front outside light, and most of the 1st floor outlets and lights all on one 14 gauge circuit, that of course the tenants had fused with a 30 amp fuse. It's a wonder the place hadn't burned down. Of course I separated the circuits and installed tamper-proof fuses, in which they still tried to cram in oversized fuses!
So then the question would be … if Square D breakers allow a double tap, then how would the breaker know one wire is overloaded? Even though the breaker may permit two wires, its still a double tap, and the load conditions would not be any different than a breaker not designed for two wires? Right?
The term “double tap” implies an “improper condition.” If the breaker is designed for two conductors, it is not considered “double tapped” when properly connected. The NEC does not (as far as I am aware) recognize the term “double tap.”
If the conductors are sized properly for the breaker, an overload would occur if the total current exceeds the breaker rating, regardless if the current is loaded on one circuit or both - the conductor is properly protected.
Nuisance trips could occur if two circuits that are heavily used are connected at one breaker designed for two conductors (or at a double tapped breaker). Two separate circuits drawing 8 amps each would trip the 15 amp breaker even though the conductor is only at 50% of it's rated capacity.
-- Jeff Pope
(661) 212-0738
a double tap with both wires firmly connected and undamaged would be an actual hazard, whether or not the breaker or fuse was specifically designed to accommodate 2 wires.
There are many things that I don’t understand about electrical and the NEC, but rather than try and figure it out, I let it be.
The NEC says components are to be used in accordance with manufacturers and UL Listing instructions/labeling. Breakers are rated for a specific number of conductors and are usually marked accordingly.
Now if I were to guess, I would say that a poor connection could develop over time as conductors heat and cool individually during use. Unless the circuits are identical in use and load, their temps will differ.
The chances that a perfectly balanced connection is maintained (as in your scenario) would be quite slim if the component was not specifically designed for that purpose..
-- Jeff Pope
(661) 212-0738
Originally Posted By: brian winkle This post was automatically imported from our archived forum.
It is very hard to get 2 wires to stay under a screw. Many times if you pull on a double tap one will pull out. We are forbidden to put more than one wire under any screw that is not listed for it. Plus, all screws are supposed to be torqued, how can you get a proper torque reading with 2 wires squashing around each other?
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
There seems to be 2 questions bouncing around.
The answer for connecting the surge supressor is in the manufacturer’s instructions. No place else. They make supressors for the main but most sold to the consumer market connect to the load side of a breaker on the rail. If an existing 240v breaker is listed for 2 conductors you can double tap following the instruction as to wire type and size or you could pigtail a splice to the supressor. These shunt the transient as a parallel circuit so the actual location on the rail is not really important. Personally I would make it the breaker closest to the main but you are really only talking about an extra nano-second or so, far faster than the MOV switches.
As for the double tap itself, you still come back to what the manufacturer's instructions say. There are usually going to be restrictions on stranded wires and combinations of wire sizes. RTFM
[quote=“jpope”]
230-82 exception 4
Now what?
P.S.
I was looking at the 1996 NEC.
230-82 EXCEPTION no. 4