Yeah or nay? TIA
Roy, aren’t you a retired electrician? What say you? ![]()
I do not see size or type of wire …
Retired in 1997 dropped my licence then and have no code books.
Good points…I don’t know, Josh…sorry, buddy.
But, I bet it is very close to correct.
#12 is limited to 20 amps unless for a motor or compressor load, neither of which apply.
Thanks, Jim. ![]()
Installation instructions for this unit call for 25 amp, #10 wire.
25 amp breakers are hard to find so a 30 amps will most likely be needed.
Minimum circuit size is:
4500/240=18.75*125%=23.4 amps
#12 is only good for 20 amps unless one of the load types that Jim mentioned.
#10 is the minimum conductor size and if the manufacturer’s instructions says to use a 25 amp OCPD then that is the maximum OCPD size. Typically these are fed with #10 conductors on a 30 amp circuit.