My question - why is a 30 ampere breaker with 10 AWG wire required to feed an electric water heater, when the wires in the heater itself are undoubtedly 12 AWG?
What am I not thinking of on this. Seems that it should be a 20 ampere breaker with 12 AWG wire or the water heater should have 10 AWG wire.
Electrician Side Note…I don’t care much for this image because the verbage as changed from the 2002 NEC to the 2005 NEC…while we are in the 2002 NEC here my verbage is correct…but the image is more catered to the 2005 NEC…
Basically the same…verbage different…the addition clarrification to allow minimum 125% rated of the OCPD but not the exceed the 150% rating as well…kinda don’t like how they re-wrote that …but who am I to tell the code panels how to write something…I am just a member of the POSSE’
FYI…yes you could put a waterheater on a 25A 2 pole breaker if you want…still has to be 10 AWG wire…anyway it is late and I am rambling now…Later
Actually JOHN…you should use a title like…“Electrical Masters and Rulers of the UNIVERSE” in the subject line versus…Hey Sparky’s…we are a sensative bunch…
You also need to remember #12 is really good for 25a in 310.16. It is only 240.4(D) that has us thinking 20a. a 5500w water heater is only 23a or so. At the few feet a wire runs in a water heater this is negligible heating, where we are looking for heat in the first place.
FYI running the next size larger wire is a good idea for major draw appliances. You still have to fuse it correctly for the appliance though. It will save $$$ over time because of the lesser resistance of the wire. Motors will last longer, and the KWH on the meter will be a little bit less.:shock: :shock: