Aluminum wire bonded to water pipe

Originally Posted By: cowen
This post was automatically imported from our archived forum.



Can the electrical panel be bonded to a water pipe with aluminum wiring? Also the aluminum wire was clamped to the copper water pipe with an aluminum clamp.


Originally Posted By: jpope
This post was automatically imported from our archived forum.



Aluminum conductors are allowed for use in the GEC system per NEC 250.66.


The clamp is required to be listed for the specific application (250.70)


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: Jay Moge
This post was automatically imported from our archived forum.



i’ve only actualy seen copper bonds. i’d wonder if the aluminum to copper connection at the clamp would cause some dissimalar metal currosion and increase the resistance and lessen the effectivness of the ground. what is the house wiring? al. or copper. i’m sure the panel itself is steel. not sure maybe one of our resident sparkies will help. icon_cool.gif


Originally Posted By: Jay Moge
This post was automatically imported from our archived forum.



sorry Jeff i was typing while you were posting and didn’t see you till i posted. icon_cool.gif


Originally Posted By: jpope
This post was automatically imported from our archived forum.



The aluminum conductor must be sized appropriately as well. The minimum size would be 6 awg and would increase based on the size of the ungrounded service entrance conductors (SEC).



Jeff Pope


JPI Home Inspection Service


“At JPI, we’ll help you look better”


(661) 212-0738

Originally Posted By: joetedesco
This post was automatically imported from our archived forum.



250.64 Grounding Electrode Conductor Installation


(A) Where used outside, aluminum or copper-clad aluminum grounding conductors shall not be terminated within 450 mm (18 in.) of the earth.

250.120 Equipment Grounding Conductor Installation

(B) Aluminum and Copper-Clad Aluminum Conductors Equipment grounding conductors of bare or insulated aluminum or copper-clad aluminum shall be permitted.

Bare conductors shall not come in direct contact with masonry or the earth or where subject to corrosive conditions. Aluminum or copper-clad aluminum conductors shall not be terminated within 450 mm (18 in.) of the earth.


--
Joe Tedesco, Massachusetts
Home Inspector Provider
www.joetedesco.org
necmeister@gmail.com

www.nachi.org/tedesco.htm
www.nachi.org/tedesco2.htm
www.nachi.org/illinoislicense.htm
www.nachi.org/jtarticles.htm

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



joetedesco wrote:
250.120 Equipment Grounding Conductor Installation

(B) Aluminum and Copper-Clad Aluminum Conductors Equipment grounding conductors of bare or insulated aluminum or copper-clad aluminum shall be permitted.

Bare conductors shall not come in direct contact with masonry or the earth or where subject to corrosive conditions. Aluminum or copper-clad aluminum conductors shall not be terminated within 450 mm (18 in.) of the earth.


To be clear 250.120 does not apply to a GEC. ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)

250.120 only applies to equipment grounding conductors.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: joetedesco
This post was automatically imported from our archived forum.



Bob:


Correct, but the rule is the same, we know it is not a GEC, but the rule is applicable to the EGC.

This was to provide information that can be used when the question arises.

![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)


--
Joe Tedesco, Massachusetts
Home Inspector Provider
www.joetedesco.org
necmeister@gmail.com

www.nachi.org/tedesco.htm
www.nachi.org/tedesco2.htm
www.nachi.org/illinoislicense.htm
www.nachi.org/jtarticles.htm

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Thats cool Joe, but the rules are not the same.


250.64 only applies outside.

So in a basement I can terminate an AL GEC down at floor level if need be, some water services come in very low.

AL could also be in contact with the masonry. I agree a bad idea but as always the NEC is a minimum.

Perhaps a proposal is in order?

Personally I very rarely use AL anyway. ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: joetedesco
This post was automatically imported from our archived forum.



Bob:


I see your point, in a basement the use of aluminum would probably not last too long at all.

My mother in-law had a situation where the clamp was attached on the water pipe near the basement floor. It rusted out bad, and the connection would never have served its purpose if it was called upon to do its job. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)


--
Joe Tedesco, Massachusetts