Originally Posted By: cowen This post was automatically imported from our archived forum.
Can the electrical panel be bonded to a water pipe with aluminum wiring? Also the aluminum wire was clamped to the copper water pipe with an aluminum clamp.
Originally Posted By: Jay Moge This post was automatically imported from our archived forum.
i’ve only actualy seen copper bonds. i’d wonder if the aluminum to copper connection at the clamp would cause some dissimalar metal currosion and increase the resistance and lessen the effectivness of the ground. what is the house wiring? al. or copper. i’m sure the panel itself is steel. not sure maybe one of our resident sparkies will help.
Originally Posted By: jpope This post was automatically imported from our archived forum.
The aluminum conductor must be sized appropriately as well. The minimum size would be 6 awg and would increase based on the size of the ungrounded service entrance conductors (SEC).
(B) Aluminum and Copper-Clad Aluminum Conductors Equipment grounding conductors of bare or insulated aluminum or copper-clad aluminum shall be permitted.
Bare conductors shall not come in direct contact with masonry or the earth or where subject to corrosive conditions. Aluminum or copper-clad aluminum conductors shall not be terminated within 450 mm (18 in.) of the earth.
(B) Aluminum and Copper-Clad Aluminum Conductors Equipment grounding conductors of bare or insulated aluminum or copper-clad aluminum shall be permitted.
Bare conductors shall not come in direct contact with masonry or the earth or where subject to corrosive conditions. Aluminum or copper-clad aluminum conductors shall not be terminated within 450 mm (18 in.) of the earth.
To be clear 250.120 does not apply to a GEC. ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)
250.120 only applies to equipment grounding conductors.
-- Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
Originally Posted By: joetedesco This post was automatically imported from our archived forum.
Bob:
I see your point, in a basement the use of aluminum would probably not last too long at all.
My mother in-law had a situation where the clamp was attached on the water pipe near the basement floor. It rusted out bad, and the connection would never have served its purpose if it was called upon to do its job. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)